On Tue, 24 Jul 2007 09:02:39 -0700, w_tom <w_tom1@usa.net> put finger
to keyboard and composed:
I
| +I ^
| |
| |
-V ______0_____| +V ---> V
|
|
|
| -I
Nowhere is the resistance (R=V/I) of the protector equal to zero.
This is the IV characteristic of a perfect wire, ie one with zero
resistance:
I
| +I ^
| |
| |
|V=0 ---> V
|
|
|
| -I
is being shunted to earth.
generator terminals in an airplane utilises an earth connection?
bond in a MEN system. A surge suppressor between A-N is required
because only one end of a common mode surge entering the premises is
shunted to ground at the meter box.
the nature of its design. Please place an X on the IV characteristic
curve that I have drawn above, showing any point where the absorbed
energy is zero.
characteristic, not one shaped like an ice hockey stick. And yes, it
will absorb less energy. But a 20mm MOV will only absorb 3% less
energy (your numbers) than a 7mm MOV.
only absorb about 3-5% less energy than a smaller one. The bigger MOV
is better because it will sustain larger surges without damage, and
because it can sustain more surges, not because it can reduce the
impact of the same surge current by a mere 5%.
It doesn't care where the surge current goes - it just attempts to
maintain its terminal voltage as low as possible.
- Franc Zabkar
--
Please remove one 'i' from my address when replying by email.
to keyboard and composed:
A reduction of 3% (your numbers) is insignificant.On Jul 23, 6:01 am, Franc Zabkar <fzab...@iinternode.on.net> wrote:
On Fri, 20 Jul 2007 06:39:35 -0700,w_tom<w_t...@usa.net> put finger
You cannot seriously claim that a figure of 3% or 5% is significant.
It amounts to *nothing*. It is certainly not a valid reason to choose
a higher energy MOV over a lower energy one. It makes about as much
sense as choosing a 5W zener over a 400mW zener when the circuit
dissipation calls for 100mW. The benefits of a larger MOV are an
ability to withstand a larger surge, and an ability to withstand more
surges in the same time. The latter is reflected in the average power
rating.
Again the point is being avoided - a point directly traceable to
Tim's original question. Franc claims shunt mode protectors work by
absorbing surges. In each case, a better protector absorbs less
energy. MOVs with more joules absorb less energy.
E = Vp x Ip x dt for *all* shunt mode protectors.Replacing MOVs
with avalanche diodes absorb even less energy. Using a gas discharge
tube (as was the standard solution almost 100 years ago) absorbs even
less energy,
What will happen if you place a wire across a mains supply?Absorbing less energy is what a shunt mode protector
does - equivalent to what a wire does.
This is the IV characteristic of a perfect shunt mode protector:Energy is shunted (diverted,
clamped, connected) elsewhere. That 'elsewhere' is earth ground.
I
| +I ^
| |
| |
-V ______0_____| +V ---> V
|
|
|
| -I
Nowhere is the resistance (R=V/I) of the protector equal to zero.
This is the IV characteristic of a perfect wire, ie one with zero
resistance:
I
| +I ^
| |
| |
|V=0 ---> V
|
|
|
| -I
Earthing is irrelevant to a shunt mode system, unless the surge/spikeBud so dislikes this reality because his protectors don't have a low
impedance earthing connection. Why is earthing THE most critical
component in a shunt mode 'system'?
is being shunted to earth.
Energy does *not* pass mysteriously through a MOV on its way to earth.An MOV, et al becomes as
conductive as possible. A surge is shunted (clamped, diverted) to
earth ground. Earth dissipates the surge - not a protector. An MOV
that shunts 20 or 30 times more energy to earth (than is absorbed) is
a best protector for the dollar.
Explain how a shunt mode protector (eg transorb) connected across theMOV does not protect by absorbing surge energy. MOV protects by
shunting that energy elsewhere - into earth.
generator terminals in an airplane utilises an earth connection?
A two-wire appliance has no earth ground other than the earth-neutralThe bottom line about surge protection:
Only component required in a surge protection system is earth ground.
bond in a MEN system. A surge suppressor between A-N is required
because only one end of a common mode surge entering the premises is
shunted to ground at the meter box.
A *perfect* shunt mode protector *always* absorbs energy. That's inEither a surge is connected directly to earth OR we install an MOV
type protector to make a temporary earthing connection. Earthing
electrode is the 'protection'. 'Protector' is either a hard wire
(cable TV or satellite dish) or a 'whole house' type protector (for
telephone or AC electric).
MOV and wire only absorb energy because each is not perfect.
the nature of its design. Please place an X on the IV characteristic
curve that I have drawn above, showing any point where the absorbed
energy is zero.
Yes, a better shunt mode protector will have a vertical IVBoth
absorb trivial energy to shunt massive energy elsewhere. Both become
even better protectors when they absorb less energy. Franc - that is
the point. Better protectors in every case absorb less energy.
characteristic, not one shaped like an ice hockey stick. And yes, it
will absorb less energy. But a 20mm MOV will only absorb 3% less
energy (your numbers) than a 7mm MOV.
I have *never* claimed that. I have always said that a bigger MOV willMore
joules in an MOV means it absorbs less energy - especially when the
MOV is so grossly undersized as to operate at the end of that hock
stick upswing. Why do you keep trying to claim a better protector
will absorb more surge energy? Why do you keep arguing irrelevance?
only absorb about 3-5% less energy than a smaller one. The bigger MOV
is better because it will sustain larger surges without damage, and
because it can sustain more surges, not because it can reduce the
impact of the same surge current by a mere 5%.
A MOV is only interested in the potential between its two terminals.Tim asked whether a surge protector was recommended. Yes, but one
that earths surges. One that is sufficiently size so as to be a
better conductor - not create these scary pictures:
http://www.hanford.gov/rl/?page=556&parent=554
http://www.westwhitelandfire.com/Articles/Surge%20Protectors.pdf
http://www.ddxg.net/old/surge_protectors.htm
http://www.zerosurge.com/HTML/movs.html
Since an MOV operates by shunting (absorbing less energy), then the
protector will only be as effective as its earth ground. Earth is
where energy is absorbed. No earth ground means an MOV has nothing to
shunt to - provides no effective protection. Tim should install a
protector that actually earths surges - by becoming as conductive as
is practicable.
It doesn't care where the surge current goes - it just attempts to
maintain its terminal voltage as low as possible.
- Franc Zabkar
--
Please remove one 'i' from my address when replying by email.