lightning protection

Halfgaar <voor_achter@nospam.com> wrote in message news:<3f26f569$0$143$edd6591c@news.versatel.net>...
tube2ic wrote:

A good quality surge supressor, would have at least one common mode
choke (A black ferrite ring) with thick wire wound on it with 4 wires
connected across the input. At least 2 high voltage capacitors and a
fairly big (the size of a dime) thing that looks like a capacitor
(which is probably an MOV-Metal Oxide Varistor). Also it should have a
three pin plug. No doubt there are other designs as well.
While a good ground is a good thing, it is not necessary to get too
paranoid about it. Just make sure that it is connected to the socket
that you are using. You can check by connecting a meter between phase
and ground and between phase and neutral. If the difference is no more
than 2 Volts, your ground is adequate.

I'll check the parts sometime.

Won't measuring the phase and the ground create a leakage so that the "earth
leakage breaker" (I don't know what it's called in English) will disconnect
power?

Halfgaar
No. A voltmeter is high impedance. If you use a lamp then it would
probably trip. (Depends on your system)
 
On Mon, 28 Jul 2003 20:19:40 +0100, Sir Charles W. Shults III wrote:

Fulgurites.
That's the one! Thanks.
--
Then there's duct tape ...
(Garrison Keillor)
nofr@sbhevre.pbzchyvax.pb.hx
 
I still don't know what your 750 volt 1250 amp device is.
But we know it is not an effective surge protector. Posted
previously on 26 Jul:
Which again demonstrates why 'point of use' protectors are so
ineffective. Since they don't provide effective protection,
then there is no dedicated (less than 10 foot) connection to
earth AND those ineffective protectors avoid all discussion
about earthing.
If it does not have the less than 10 foot earth ground
connection OR it does not even discuss earthing, then it
probably provides no such protection. Identifying ineffective
protectors is that simple. Furthermore implied, it is an
electromechanical device. Again, cannot protect from hardware
destruction. Too slow. Remember the microsecond destruction
followed eons later by the millisecond response of that
device?

It might be doing something else. But it is not protecting
electronics from potentially destructive transients.
Conditions repeated in that first paragraph make it obvious
what the device cannot do.

In the meantime, where are contradictory responses. Only
one provided blunt technical facts that say that device
provides no transient protection AND could not do so. Facts
with numbers such as microsecond destructive transients that
cannot be stopped by a millisecond responding device.

First provide some specific claims, with technical numbers,
that says what the device does. Currently, we don't even know
what it is suppose to do. Claims without numbers is more akin
to junk science. What technically does that parasitic device
even claim to do? We know what it cannot do. What does it
claim to do?

Halfgaar wrote:
I seem to be getting several conflicting answers here.

Basicly, all I'd like to know is: can I trust the surge protector (or
"parasite eliminator" or something as the manufacturer calls it) in my
extension cord (or power strip or whatever) to protect my equipment? Does
it at least do *any* good, or can I just leave it out?

This discussion is getting somewhat big, so I'd like a definate answer :)
 
... the surge that is travelling that same distance to the
surge protector on the phase will be attenuated by the same
amount won't it?
Surges are ideal current sources; not voltage sources.
Incoming surge will increase voltage as necessary to get to
the appliance or earth ground. But surge protection is about
making a lower voltage connection to earth. Less voltage
(because current is shunted to earth on a low impedance
connection) means a surge (now at less voltage) will not seek
alternative destructive paths through appliances. But too
much impedance to earth ground (such as through wall
receptacle outlets) means the surge must find destructive
paths via adjacent appliances. This is basic circuit theory.

Knowledge of basic circuit theory would have made that
obvious. Bottom line, surge protection is about earthing a
surge before it can enter the building. Once inside the
building, destructive current flows can be everywhere. Far
too complex to justify the analysis or to be solved with
simple plug-in solutions. Best to earth a surge at the
service entrance and be done with it - at far less expense.

Misrepresented is the cost of 'whole house' protection. A
plug-in protector for only one appliance may cost $15 or $50
per appliance. The 'whole house' protector costs maybe $1 per
protected appliance. The so low cost of effective 'whole
house' protectors that makes 'whole house' protection a good
investment for the event that typically occurs once every
eight years.

Why does the telco install 'whole house' protector on your
premise interface? Because and again, the 'whole house'
protector is so inexpensive, so effective, and not a grossly
overpriced $25 for one appliance. Telcos don't waste money
because they are big companies. The smart money also installs
a 'whole house' protector on AC electric for that $800
computer and the other 100 other household appliances. What
protects that furnace, dishwasher, dimmer switch, and bathroom
GFCI for human safety? No plug-in surge protector even claims
to provide that protection.

I suspect you are totally lost on too much information and
not enough technical background, as indicated by recommending
sources such as PG&E. Where are the technical numbers at PG&E
(a company so short of technical competence that its President
was a lawyer who did not even understand why future markets
are essential to utilities). I tried to keep it simple.
Provided was only enough to introduce concepts - why 'whole
house' protectors are so effective and why plug-in protectors
are not sufficient (as well as grossly overpriced). Provided
was information from application notes for further study. But
if you think that anything posted was learned solely from
application notes? Probability says I have been building and
experimenting with surge protectors before most here even
existed. To tell me that the plug-in surge protector is
effective without comprehension even of basic circuit theory
is rather discourteous.

The more expensive and least effective surge protector
solution is that $25 plug-in protector. It does not even
claim protection that so many wish it to provide. Of course
not. It must avoid this quote that should sound familiar:
... your surge protector will work by diverting surges to earth.
The best surge protector in the world can be useless if grounding
is not done properly.
Instead, plug-in protectors must avoid all discussion about
grounding to sell their products at an excessive $25.

tube2ic wrote:
w_tom <w_tom1@hotmail.com> wrote in message news:<3F28370D.84617975@hotmail.com>...
The reason why a typical plug-in protector has no effective
earth ground connection (via green safety ground wire or white
neutral wire) is that wire has impedance. A 50 foot 20 amp
wire measuring 0.2 ohms resistance may also be 130 ohms
impedance to a surge current. Sufficient to safety ground 60
Hz power (20 amps times .02 ohms is less than 1 volt) but
insufficient to earth a surge (100 amps times 130 ohms is
13,000 volts).
No offence but you are throwing a lot of information that you got from
application notes. While the information is essentially correct, you
are misinterpreting most of it. If I am too far from ground that wire
impedance is making it ineffective as you say, then by the same token,
the surge that is travelling that same distance to the surge protector
on the phase will be attenuated by the same amount won't it? So if the
surge protector is one end of a 50ft wire and you surge the other end,
then by your calculation, it would drop 13KV. So unless the surge was
greater than 13KV, there would be no problem right?
"Hotdamn Paw fergit the Purtector! I'm a gonna steal me 50 ft of
wire."

Wire impedance is why the telco installs their 'whole house'
protectors where wires enter building directly on earth ground
AND prefer a 50 meter separation between protector and
switching computer. The impedance in 50 meter wire adds more
protection to the surge protection circuit. Their 'whole
house' protector has near zero impedance to earth ground and
maybe 100+ ohms impedance to $multimillion computer. If they
located surge protector next to computer, then that 100+ ohm
wire impedance back to earth ground would result in switching
computer damage.
My computer only costs about 800 bucks. Am I going to install
equipment and a ground worth a couple of thousand (plus installation),
to protect something that is worth less than that? Or am I going to
walk into Fry's and pick up a 25 buck spike supressor? A TELCO can
afford to do a lot of things. When the CEO of a TELCO wants to travel,
he flies in a Lear jet. Me..I take the bus.


Internal choke actually has a function different from what
many assume. Too many assume it is to filter the surge. Yes,
but not for reasons assumed. I believe Littelfuse
applications notes explain it best. That choke can slow a
rising edge of a large transient. By lengthening the surge, a
MOV is less likely to vaporize on a single massive surge.
Choke inductance is really not much of a filter. But it will
dampen the rising edge of a 100+ amp, single microsecond, type
transient. Dampen enough that the MOV has a better chance of
survival - not become a short circuit. Another way to
accomplish same is to simply install more MOVs - increase
joules.

Again this depends on the design. There are many tpes of protection
devices. Typically semiconductor based devices such as Diacs or Sidacs
have snubber circuits which function as you describe above. MOVs could
have them too but for an entirely different reason. However what you
are describing as "choke inductance" is different from the common-mode
choke which is a filter.
The reason why MOV's are paralleled is because the cost of the MOV
exponentially rises with its capacity to handle energy (The Joules you
keep talking about which you claim can determine my life expectancy
:) (BTW Joules is a unit of Energy). So it is cheaper to build a
suppressor with 10 MOVs of smaller capacity than with one MOV with 10
times that capacity. The trick is to get them all to fire at the same
instance. If one fires before the others, then all the energy would
flow through that one device and destroy it. If you put an inductor
before all of them, it allows the gradual build up of energy and helps
in minimizing the above effect.


However if wire impedance back to earth ground approaches or
exceeds 100 ohms, then no effective earth ground exists
anyway. This is the problem with plug-in protection. It has
all but no earth ground due to wire impedance, too many wire
splices, many sharp bends, possibly inside conduit, bundled
with other non-earthing wire, etc. All mean the plug-in
protector does not have a prerequisite and effective
connection to central earth ground. Wire impedance is so
important to surge protection that Littelfuse even discusses
wire impedance of 2 inch leads on their MOVs. Even wire
length on MOVs affect impedance and testing numbers. Wire
impedance is why plug-in protectors have all but no earth
ground connection. Wire impedance is why the less than 10
foot connection is so important.
Hey man did you move your house to your Utility's Power Generation
station? They have the best ground. If you ask them nicely, them may
let you set up camp 2 inches away from it. No offence Tom. You are an
intelligent person reading something from some websites and then boom!
You wind up with some explanation that I find hard to read without
bursting into laughter. Yet you claim to have two EE degrees at some
other post. Anyway I will take you at your word. If you got EE then
you can follow this stuff.
http://www.itu.int/rec/recommendation.asp?type=folders&lang=e&parent=T-REC-K.11
The above is a link to an ITU-T recommendation entitled "Principles of
protection against overvoltages and overcurrents"
This and some of the other K series documents is what I refer to when
I design protection circuitry. (By the way if you register, you can
download 3 standards free)
Also don't forget to read NIST's recommendataions on Surge protection
http://www.nist.gov/public_affairs/practiceguides/surgesfnl.pdf
Another good and practical guide to surge protetction is your local
PG&E website.

Joules in a surge protector can determine life expectancy.
But quality of earth ground determines how effective the
'system' is during one surge. Superior earthing is why one of
my experiments so effectively protected an entire half of a
house using only one 70 joule MOV. Believe me. I was
completely amazed. Entire circuit from AC main to earth
ground in conductive soil was about 2 feet. Surge protector
made effective by earth ground including the short connection.

Primary function of a surge protector is to protect any humans. Its
secondary function is to protect the circuits downstream. If it can
protect itself while doing so, that's a bonus.

tube2ic wrote:
w_tom <w_tom1@hotmail.com> wrote in message news:<3F267D26.CEEC344D@hotmail.com>...
Now provide the inductance of that choke - the numbers.
Ironically, an electronic appliance must already have a
superior in-line choke filter. In other threads, some bought
cheap power supplies that did not have that required filter.
The resulting radio interference was completely unaffected by
a surge protector with filter choke - because that surge
protector filter choke is simply too small.

A common mode choke is actually a transformer. It's function is to
attenuate AC noise (greater than mains frequency) that affects both
phase and neutral equally using phase cancellation techniques.(Hence
the name common-mode choke).
These chokes are not designed based on their incductance as that is
not very high given their few turns and thick wire. They are designed
based on the ammount of current they have to carry as each winding is
in series with the load.
Unless your electronic appliance uses a switch mode power supply,
(Like a computer etc.), it is not mandatory to have this choke within
the appliance.

Surge protectors do not stop, block, or absorb surges. They
are called shunt mode devices for good reason. Their job is
to simply shunt (connect, distribute, short) a surge from one
wire to all others. No short, dedicated, and independent
connection to earth ground means the plug-in surge protector
only provides a destructive surge with more paths to find
earth ground - destructively through adjacent appliances.

I think you and I are on the same side here in that surge protectors
do not stop, block or absorb surges. They do indeed shunt or short the
surge as I have explained elsewhere in these posts. They do however
reduce the surge energy and thus protect the device they are connected
to. However, they do not do so from "one wire to all others" as you
say. A good surge protector as I have already mentioned, uses the
ground connector to discharge the surge energy. However, it is
perfectly acceptable to discharge this wrt neutral. As the purpose is
to protect the equipment downstream of the surge-protector. However,
you cannot use a 3 pin surge supressor on a 2 pin socket as the surge
circuitry would be effectively disconnected or now fire at double the
designed voltage depending on the design.

I think that we are at cross purposes here as to the scale of the
surge supressor. For a whole-house supressor, which is located at the
input of the AC mains to the house, by all means have an independent
ground. It is most probably required for a correct installation.

However, I entered this list at Halfgaar's question about a Surge
Protector Strip and those protectors do not require an independent
connection to ground.
Most engineering is a compromise between practicality, cost and
pragmatism. What is the cost of a professionally installed earth
ground? What is the cost of the TV set or stereo that you are
protecting? Which is more expensive? Also are you going to install all
the electronic/electrical equipment in your house in a tight circle
around the ground rod?
I am not denying the usefulness of a good ground. Just don't get
carried away by it.


A good quality surge supressor notes the critical importance
of earthing. Benchmarks in surge protection, such as
Polyphaser, don't discuss their product line in application
notes. Polyphaser discusses the most critical component in
any surge protection 'system' - central earth ground:
http://www.polyphaser.com/ppc_pen_home.asp

How important is earthing to Polyphaser? A product does not
even have a connection to earth ground. Distance to earth
must be so short that the Polyphaser product mounts directly
ON earth ground. But then those who know surge protector know
that Polyphaser is an industry benchmark. Therefore
Polyphaser discusses earthing - extensively.

No earth ground means no effective surge protection. So
plug-in protectors lie by telling half truths. They avoid all
discussion about earthing since they have none. A surge
protector is only as effective as its earth ground.

All this is probably quite true for a large scale surge suppressors
but probably not relevant to Halfgaar's Surge Protector. Believe me.
If it was, then there would be another regulatory requirement for it.
Again I reiterate a good ground is great but an adequate ground, does
the job.
 
Halfgaar <voor_achter@nospam.com> wrote in message news:<3f285520$0$134$edd6591c@news.versatel.net>...
I seem to be getting several conflicting answers here.

Basicly, all I'd like to know is: can I trust the surge protector (or
"parasite eliminator" or something as the manufacturer calls it) in my
extension cord (or power strip or whatever) to protect my equipment? Does
it at least do *any* good, or can I just leave it out?

This discussion is getting somewhat big, so I'd like a definate answer :)

Halfgaar
Halgaar,
It is unfortunately the nature of a newsgroup to give you anything but
a definite answer.
I strongly urge you to read this brochure for the layman by National
Institute of Standards and Technology (US Dept of Commerce).
http://www.nist.gov/public_affairs/practiceguides/surgesfnl.pdf

You should also look at the website of your local utility company for
information. These are un-biased independent bodies which tell it
plain vanilla.

To give credit to Tom, he is not telling anything that conflicts too
much with what I am saying. It is the details that are off and can
mislead a layman. The facts that he quotes from application notes are
obviously correct. The only thing that he doesn't get is that surge
protectors are classifed into grades, classes and work in different
modes, based on their design, scale, type of protection. What he is
talking about are service panel surge protectors for whole house or
even a metering-panel protector that is installed by utility companies
in areas of strong lightning activity. What you are asking about are
called plug-in surge protectors. They do work if they are properly
designed. Unfortunately with the information you have provided, there
is no way to tell if yours is properly designed. Should you leave it
out? Maybe not because even if it does half of what it's supposed to
do, it's still better than nothing. But is it guaranteed to work? Hard
to say. You have to be aware of the risks.

Also it is always dangerous to have independent earth grounds due to a
phenomenon called ground bounce. All grounds have to be tied to a
common point to earth ground using special very thick bonding
conductors that are low impedance which nullify all the effects he
keeps talking about. (Little knowledge is a dangerous thing). Do you
seriously imagine that Utilities, Telcos and Government agencies do
not give any though about these things? There is a regulation/standard
for everything.

Thirdly all lightning rods are not created equal. There are types
which are proven to be ineffective. As a layman you cannot rely on the
say so of a manufacturer. You need to look for unbiased information
from organizations such as the National Lightning Safety Institue
http://www.lightningsafety.com

We need to keep things in perspective. To protect multi-million
dollars of equipment, you need to spend hundreds of thousands of
dollars in surge protection. To protect a thousand dollar appliance
you need to spend a hundred or less.
Is the hundreds of thousand dollar protector better than the hundred
dollar one? You bet your life it is. So are you going to go buy the
former? A fine fool you will look if an indirect lightning stike
destroyed your thousand dollar protector in saving your 300 dollar TV.

Lastly, lightning as a phenomenon is still not understood fully. There
are several groups of researchers that are at loggerheads with each
other. So until there is agreement by the experts, there will always
be conflicting opinions.

Hope this helps. I will not post further to this list as I have a new
project. I have to design lightning protection for some mobile
wireless equipment that will keep me in the lab zapping equipment for
several weeks. Ta Ta Halfgaar all the best in your quest.
 
On Tue, 29 Jul 2003 23:30:09 +0100, Halfgaar wrote:

"earth leakage breaker" (I don't know what it's called in English)
Depends where you live:

"Ground fault current interrupter" (GFCI) in North America.

"Earth leakage circuit breaker" (ELCB), now obsoleted by "Residual
current circuit breaker" (RCCB), or "Residual current device" (RCD), in
the UK.

--
Then there's duct tape ...
(Garrison Keillor)
nofr@sbhevre.pbzchyvax.pb.hx
 
w_tom wrote:

I still don't know what your 750 volt 1250 amp device is.
But we know it is not an effective surge protector. Posted
previously on 26 Jul:
Which again demonstrates why 'point of use' protectors are so
ineffective. Since they don't provide effective protection,
then there is no dedicated (less than 10 foot) connection to
earth AND those ineffective protectors avoid all discussion
about earthing.

If it does not have the less than 10 foot earth ground
connection OR it does not even discuss earthing, then it
probably provides no such protection. Identifying ineffective
protectors is that simple. Furthermore implied, it is an
electromechanical device. Again, cannot protect from hardware
destruction. Too slow. Remember the microsecond destruction
followed eons later by the millisecond response of that
device?

It might be doing something else. But it is not protecting
electronics from potentially destructive transients.
Conditions repeated in that first paragraph make it obvious
what the device cannot do.

In the meantime, where are contradictory responses. Only
one provided blunt technical facts that say that device
provides no transient protection AND could not do so. Facts
with numbers such as microsecond destructive transients that
cannot be stopped by a millisecond responding device.

First provide some specific claims, with technical numbers,
that says what the device does. Currently, we don't even know
what it is suppose to do. Claims without numbers is more akin
to junk science. What technically does that parasitic device
even claim to do? We know what it cannot do. What does it
claim to do?
I don't really know what it's supposed to do. It was written on the box, at
least in some stupid metafor, but I don't have the box anymore.

And about the 10 ft, Tube2ic doesn't seem to think it's all that important.

I think I know all I can find out here. I'll do some more research and
hopefully find out some more.

Thanks to all for your time.

Halfgaar
--
To send email, change nospam.com into yahoo.com.
 
Halfgaar <voor_achter@nospam.com> wrote:

Is it also impossible to protect against indirect hits? I know that direct
hits are fatal, but a few days ago, I saw an add in the paper from a
company which sells protectors for indirect hits. You don't just buy the
device, but also an insurrance. If anything is damaged, they'll pay the
damages. Is this possible, or just a trick to get people to buy those
things? After all, not everyone who buys such a thing gets hit by lightning
(well, their equipment...), so maybe the devices are fake and they just
make money on the insurances.
I don't know about your particular case, but I tend to view these as
paying for the insurance not surge protection. Given that most power in
UK cities comes in underground I am extremely dubious about the value
of these devices in my enviroment. I would rather pay for better quality
plugs, sockets and cable.

I have seen one of these fail to protect its load, turned out the
"electrician" had wired up between the red & blue busbars (across
2 phases of a 3 phase line) and stuck 400V at practically unlimited
current up an alegedly 240V feed. The smoke was impressive.

Regards, Dan.
--
** The email address *IS* valid, do NOT remove the spamblock
And on the evening of the first day the lord said...........
..... LX 1, GO!; and there was light.
 
One must display knowledge of basic concepts such as
impedance, common mode transients, and etc to make a credible
claim about surge protection. Another does not yet demonstrate
knowledge of basic circuit theory or wire impedance. That
knowledge is necessary to understand the critical - absolutely
essential - nature ofthat 10 foot connection. How can one
demonstrate no underlying knowledge and yet be treated with
equal credibility? Did he post any of these previously posted
facts:
the relationship between joules and MOV life expectancy,
other factors that adversely increase wire impedance,
underlying principle of single point earth ground (with
examples from industry professionals),
purpose of UL, NEC, FCC and other standards,
timing relationships between response times and surge
transients,
how to test that a MOV is still effective,
myth of destructive surges from fluorescent lamps,
'OK' lamp nonsense and what it really reports,
relationship between surge protector and surge protection,
frequency of destructive transients,
effective protection has been proven everywhere since the
1930s meaning that surge damage is directly traceable to human
failure,
other protection devices including some species of trees,
appliances have internal protection (with numerical examples),
difference between a destructive surge and trivial noise,
long list of reasons why we know household appliances don't
generate destructive surges,
receptacle safety ground is a different and not earth ground,
human safety verse transistor safety,
that all so critical single point earth ground,
post 1990 NEC changes that may provide a minimally acceptable
central earth ground,
underlying geology can affect surge protection,
numerous outright errors in the penlight.org FAQ,
power supplies are RF transmitters that require AC mains
filtering (which surge protectors can't provide),
how some utilities don't even need (nor should use) surge
protectors to provide effective surge protection,
telco phone line already has effective protection,
that chokes, inductors, and filters are equivalent,
what that filter really does inside a surge protector,
wire impedance is so critical that even Littelfuse worries
about wire impedance on an MOV's 2 inch lead,
Polyphaser and their application notes,
$15 to $50 per appliance for ineffective protection verse $1
per appliance for effective protection,
and even how this all ties in direct with Ben Franklin's
original 1752 experiments.

Posted were examples *with numbers* as to how wire impedance
makes plug-in protectors ineffective. How many numbers did
another provide to prove that 10 feet is not relevant? No
numbers is akin to promoting junk science. But to provide
those numbers, knowledge of impedance calculations is
necessary.

Another says only "I don't agree" and suddenly has has equal
credibility? If he said Saddam was going to launch weapons of
mass destruction in the next 45 minutes, would you believe
him? At what point did you stop seeing the difference between
technical fact and an ill informed reply based only upon
personal feelings and insufficient technical background?

You have a fact to take to your grave. If that protector
does not make a dedicated connection OR avoids all discussion
about earthing, then it is probably ineffective. Ineffective
protectors are that easily identified. A surge protector is
only as effective as its earth ground.

A surge protector is only as effective as its earth ground.
That plug-in device has no earth ground for a long list of
reasons summarized above. At this point you should know
exactly what 'no earth ground' "is and means" to your mystery
device.


Halfgaar wrote:
I don't really know what it's supposed to do. It was written on the box, at
least in some stupid metafor, but I don't have the box anymore.

And about the 10 ft, Tube2ic doesn't seem to think it's all that important.

I think I know all I can find out here. I'll do some more research and
hopefully find out some more.

Thanks to all for your time.

Halfgaar
 
w_tom wrote:

Halfgaar only said something about impedance after it is put before
him multiple times - with numbers. He did not even challenge those
numbers. Instead he responded without numbers because either 1) he
did not understand the circuit involved, or 2) did not even know basic
circuit theory.

Provided were numerous facts from other sources include an industry
benchmark - Polyphaser. If you dispute this, then go to the web sites
of people who come from where the work gets done and confront
lightning most - such as rec.radio.amateur.antenna. Or those two
threads in the discussion among engineers in the newsgroup misc.rural
cited previously. They also use numbers. They too don't have
problems with the need for short connection to earthing. But then
they too have training AND experience with circuit theory, MOV
datasheets, wire impedance, etc. Just more facts that those who
promote plug-in protectors cannot be bothered to read or learn.

Halfgaar even cites a NIST *.pdf document. But it is written for
layman - no numbers. It makes reference to good grounding, but does
not detail that good grounding - probably because they regard the
concept too complex for layman. If Halfgaar really understood the
science behind that web site, then he would have understood that what
was posted here and what was in that NIST pdf document are in
agreement. I provided the numbers and basic science. Most important,
Halfgaar cannot use the NIST site to claim anything I said was
incorrect. They simply cited trends without numbers - a general
direction. And they too keep refering to the most important function
is surge protection - earth ground. I refined the details AND put
numbers to it. Remember what they kept saying - importance of earth
ground. They just did not define good earth ground. I did. It
includes that less than 10 foot connection.

This is a common problem, which is why junk science is so easily
promoted. Numbers that say where and why wire impedance is so critical
is not challenged and probably not understood. So instead the comment
was "that's not correct" without any engineering facts. That
challenge to the bottom line has no technical facts in support -
therefore nothing more than rumor. Missing contradictory facts nor
any numbers and equations to challenge what was posted alone should
have been enough for any layman's ears to rise up and ask why those
numbers could not be challlenged.

Most distressing question from any American. That the government
should require such things. Evil thinking. Government regulation is
only required where industries have displayed a total disregard for
the purpose of their principles, purpose of their business, and
responsibility to customers and stockholders. It is why railroad and
auto industry regulations exist. It is why the American accounting
industry cannot be trusted and must be permenantly regulated like
those other industries.

But most standards - especially the good ones - are by private or
non-profit industry standards - ie UL, CBEA, IEEE, EIA, ISO, etc.
Even standared for ATX power supplies are superior and have no
government regulation (even though many layman are so naive as to buy
computer power supplies that violate standard of even 30 years ago).
The electrical engineering and computer industry have much less
regulation than most because it has been so responsible. However,
that does leave oppurtunity for plug-in manufacturers to 'lie by
telling half truths' which they do so freely. Halfgaar has simply
demonstrated why they can sell ineffective plug-in protectors.
Halfgaar has not even defined the hows and whys of common mode verse
differential mode transients - which is critical to understand
background in that NIST pdf document.

That 'less than 10 foot' is essential. And it is quite simple. If
the ten foot wire is too long, then a surge will go off finding other
destructive paths to earth ground inside the building. Nothing
complex here. Principles even demonstrated by Franklin in 1752.
Either the flood gets a short path downstream (single point earth
ground), or it backs up into all other creeks, storm sewers,
basements, and low lying streets (everything inside the house).
I'm Halfgaar, I believe you got me mixed up with Tube2c.

Granted, It's very hard to dismiss what you're saying, seeing as how you
explain everything in detail. But as I said, I think I've found out
everything I can here. I'll just keep in mind what you've said when for
example asking about it in specialist-electronicshops (not the household
electronics shops, they don't know anything).

Also what worries me, is that if you're right, then there is no
(inexpensive) way to protect against surges and that plugin protectors are
(almost) all just junk. There will be a lot of people who feel safe but
actually are not.

Halfgaar
--
To send email, change nospam.com into yahoo.com.
 
dmills@spamblock.demon.co.uk wrote:

I don't know about your particular case, but I tend to view these as
paying for the insurance not surge protection. Given that most power in
UK cities comes in underground I am extremely dubious about the value
of these devices in my enviroment. I would rather pay for better quality
plugs, sockets and cable.
Where I come from, all cables are underground as well, but what about surges
from electronics and welding machines nearby?

I have seen one of these fail to protect its load, turned out the
"electrician" had wired up between the red & blue busbars (across
2 phases of a 3 phase line) and stuck 400V at practically unlimited
current up an alegedly 240V feed. The smoke was impressive.
Well, continuous 400V is not exactly a surge. A surge is usually hunders of
volts, as I understand it.

Regards, Dan.
Halfgaar
--
To send email, change nospam.com into yahoo.com.
 
Hi Halfgaar,

Don't waste your breath on this guy. At first I thought he was
genuinely trying to help you and had just got a few facts mixed up.
But a quick search on google groups for w_tom soon convinced me this
guy is a crock. He even got told off by some ladies at alt.sewing for
some drivel about unplugging their sewing machines during a storm and
the same drivel about whole house protectors and 10 ft grounds. To
cut a long story short, I think that this guy got his brains zapped in
due to lightning. Probably because he forgot to ground himself by
sticking a 10ft grounding rod up his backside.

It is not my nature to be offensive to anyone but this guy w_tom is
the limit. He is the epitome of everything that is bad about the
internet and newsgroups. Unreliable information that sounds just about
right to convince a layman while having no accountability for his
actions coupled with sheer volume of rubbish text and complete
disregard for the relevance of his drivel to the thread. I have yet to
see him actually answer a question!

-Tube2ic-
 
tube2ic wrote:

Hi Halfgaar,

Don't waste your breath on this guy. At first I thought he was
genuinely trying to help you and had just got a few facts mixed up.
But a quick search on google groups for w_tom soon convinced me this
guy is a crock. He even got told off by some ladies at alt.sewing for
some drivel about unplugging their sewing machines during a storm and
the same drivel about whole house protectors and 10 ft grounds. To
cut a long story short, I think that this guy got his brains zapped in
due to lightning. Probably because he forgot to ground himself by
sticking a 10ft grounding rod up his backside.

It is not my nature to be offensive to anyone but this guy w_tom is
the limit. He is the epitome of everything that is bad about the
internet and newsgroups. Unreliable information that sounds just about
right to convince a layman while having no accountability for his
actions coupled with sheer volume of rubbish text and complete
disregard for the relevance of his drivel to the thread. I have yet to
see him actually answer a question!

-Tube2ic-
From my point of view, you could easily be the one telling lies :). But fear
not, my gut already told me to trust you more then him.

BTW, just to let you know: The voltage over phase and neutral is 226 here.
The voltage over phase and ground is 226. That falls within the 2 volt
limit, wouldn't you agree :)?

Anyway, thanks for the warning.

Halfgaar
--
To send email, change nospam.com into yahoo.com.
 
w_tom <w_tom1@usa.net> wrote:

<Snip>

useless to earth borne wire surges IF not using the single point earth
ground concept. And better quality plugs, sockets, and cable would
not help.
Granted they do not help with surge protection, but in terms of increased
system reliability for a given amount of investment the case is not
anything like so clear.

Regards, Dan.
--
** The email address *IS* valid, do NOT remove the spamblock
And on the evening of the first day the lord said...........
..... LX 1, GO!; and there was light.
 
From my point of view, you could easily be the one telling lies :).
Yes! Unfortunately that is the way of the newsgroup :)
But fear not, my gut already told me to trust you more then him.
You have a smart gut there Halfgaar feed him a beer from me:)
BTW, just to let you know: The voltage over phase and neutral is 226 here.
The voltage over phase and ground is 226. That falls within the 2 volt
limit, wouldn't you agree :)?
Yes that is fine. In many countries the neutral is actually tied to
ground at a particular tie point and so there would be no difference
in voltages unless you are very far from that tie point between
neutral and ground. The tie point could be the transformer, the pole
or your utility meter, depending on the regulation for your country.
This is the reason I said a two-pin surge protector is also possible
provided that it was originally designed for two-pin operation.

------------------------------------
Another common problem that could cause damage to electronic equipment
and cause protection mechanisms to work incorrectly is the transposing
of phase and neutral at the socket. I don't know what is the standard
in your country but you should spend a few minutes checking this.
Typically the molded plugs on some appliances display this and that
may be a good starting point to verify.
If a surge protector was designed with only one shunt element between
phase and ground then plugging in such a protector into a transposed
socket would actually put the shunt element between neutral and ground
which is at the same potential and therefore would be no protection at
all. Better quality protectors have two shunt elements between each
line to ground pin.

-tube2ic
 
Where I come from, all cables are underground as well, but what about surges
from electronics and welding machines nearby?
In case of indirect lightning strikes, it does not matter whether the
cable is underground. The energy is still picked up by induction.
I have seen one of these fail to protect its load, turned out the
"electrician" had wired up between the red & blue busbars (across
2 phases of a 3 phase line) and stuck 400V at practically unlimited
current up an alegedly 240V feed. The smoke was impressive.
The shunt element in the protector is designed to fire at anywhere
between 260 to 700 volts depending on the design. It is also not
capable of contiuously shunting energy when fired. Hence a good
protector should have a series fast acting fuse which will blow as
soon as the shunt element fires and shorts out the AC mains. Otherwise
the protector will be destroyed. (Note that the fuse is really not
much help for lightning protection and it's purpose is to protect the
protector in similar situations as above e.g. if a high voltage line
fell on a utility mains wire)
Halfgaar you mentioned about the overload breaker on your protector.
If the overload breaker is wired before the surge supressor, then it
will also perform a similar function as described above. If the
overload breaker is behind the surge supressor then its primary
function will be what I already described earlier.

Well, continuous 400V is not exactly a surge. A surge is usually hunders of
volts, as I understand it.
A surge is any voltage above normal. when a surge lasts for a longer
duration, it may sometimes be called a swell. However, your case was
that of incorrect wiring and not really a surge on a normal line.
 
tube2ic wrote:

Halfgaar you mentioned about the overload breaker on your protector.
If the overload breaker is wired before the surge supressor, then it
will also perform a similar function as described above. If the
overload breaker is behind the surge supressor then its primary
function will be what I already described earlier.
Well, to find that out, I have to open it up. It at least is psysicly
closest to the powerinlet, so I would guess the power goes trough that one
first.

Halfgaar
--
To send email, change nospam.com into yahoo.com.
 
I don't know about other countries, but here you can plug in a plug two
ways, so I would suspect that surgeprotectors meant for use here, are
designed with more than one shunt element.
I would not assume that. It is a simple matter to open it and check.
That way you will be absolutely certain.
BTW, something I was still wondering: When a surge is shunted, does that
mean that power is interrupted for a very short time?
The typical devices used as shunting element are voltage sensitive.
This means that at normal voltage they are very high impedance (Open
circuit). When a surge reaches the voltage at which the device
activates, the device goes into low impedance state (short circuit).
As soon as the voltage drops to normal, the device stops conducting
and goes back into open circuit state. This clamps the voltage at the
firing voltage of the device during a fault condition. Now if there is
a fuse or breaker and the surge is long enough in duration, the shunt
element (which is actually shorting your AC mains) will cause enough
current to flow that will cause the fuse to blow or breaker to trip
and thus interrupt the supply and protect the shunt element. If the
surge is short duration, the short is momentary and does not blow the
fuse or trip the breaker. (This is because a fuse or breaker responds
relatively slowly to the fault condition) so all that will happen is
that the voltage clamps to the firing voltage of the shunt element.
(And you will hear horrible farts in your stereo system :)
Sometimes people replace the fuse with one of a wrong rating or
response time (Or there isn't a fuse) and this results in spectacular
fireworks as the shunt device is destroyed due to the high currents
flowing through it.

I also found a website that explains surge protectors in fairly simple
terms (No numbers to satiate our friend w_tom :) but should do well
for you)
http://computer.howstuffworks.com/surge-protector.htm
The explanation is fairly simplistic in that it assumes a number of
things but it give a good enough picture of what goes on inside the
protector.

-tube2ic-
 
In the previous post, where I describe the destruction of the shunt
element due to wrong or no fuse, I want to clarify that this happens
for the longer duration surges that allow enough current to flow that
is lethal to the shunt element.
 
tube2ic wrote:

I don't know about other countries, but here you can plug in a plug two
ways, so I would suspect that surgeprotectors meant for use here, are
designed with more than one shunt element.
I would not assume that. It is a simple matter to open it and check.
That way you will be absolutely certain.
And how exactly do I identify a shunt element? How can I see if there are
more? If it's connected two phase, neutral and ground, does that mean it's
OK?

I'll think I'll open it tonight, after I've shut down all my equipment, and
have a look. A while back, you also gave me a description of what a
reasonable surgeprotector would look like, I still have to check that out.

The typical devices used as shunting element are voltage sensitive.
This means that at normal voltage they are very high impedance (Open
circuit). When a surge reaches the voltage at which the device
activates, the device goes into low impedance state (short circuit).
As soon as the voltage drops to normal, the device stops conducting
and goes back into open circuit state. This clamps the voltage at the
firing voltage of the device during a fault condition. Now if there is
a fuse or breaker and the surge is long enough in duration, the shunt
element (which is actually shorting your AC mains) will cause enough
current to flow that will cause the fuse to blow or breaker to trip
and thus interrupt the supply and protect the shunt element. If the
surge is short duration, the short is momentary and does not blow the
fuse or trip the breaker. (This is because a fuse or breaker responds
relatively slowly to the fault condition) so all that will happen is
that the voltage clamps to the firing voltage of the shunt element.
(And you will hear horrible farts in your stereo system :)
Sometimes people replace the fuse with one of a wrong rating or
response time (Or there isn't a fuse) and this results in spectacular
fireworks as the shunt device is destroyed due to the high currents
flowing through it.
Won't the short powerinteruption be destructive to the devices connected to
it? My monitor for example won't power on immediatly when you turn it on
after you've switched it off. You have to wait a few seconds, it's for
protection.

I also found a website that explains surge protectors in fairly simple
terms (No numbers to satiate our friend w_tom :) but should do well
for you)
http://computer.howstuffworks.com/surge-protector.htm
The explanation is fairly simplistic in that it assumes a number of
things but it give a good enough picture of what goes on inside the
protector.
Now why didn't I think of that. I know of the howstuffworks website. Thanks,
I'll take a look at it.

In the previous post, where I describe the destruction of the shunt
element due to wrong or no fuse, I want to clarify that this happens
for the longer duration surges that allow enough current to flow that
is lethal to the shunt element.
I gathered as much.

Halfgaar
--
To send email, change nospam.com into yahoo.com.
 