Situation is a block of units with shared external laundries. Each unit
has a switch internally that energises a power point in the external
laundry.

Is it (easilyishly) possible to install a lamp (something that clips
into a standard switchplate would be nice) that illuminates only when
current is being drawn through that circuit?

The object being not only a reminder that the circuit is live (via
lamp 'A') but also a convenient tell-tale as to when a run of
washing is complete (ie: when the machine stops drawing current).

(Of course, I'm stuffed if it turns out that the machines draw
current all the time - I will check that!)

TIA,


GB
--
"Most police misconduct occurs when citizens challenge an individual
officer's authority" (Reiss, 1971 c.in Jermier & Berkes 1979)
 
GB <gb0807@kickindanuts.threefiddy.com> wrote:

Situation is a block of units with shared external laundries. Each unit
has a switch internally that energises a power point in the external
laundry.

Is it (easilyishly) possible to install a lamp (something that clips
into a standard switchplate would be nice) that illuminates only when
current is being drawn through that circuit?

The object being not only a reminder that the circuit is live (via
lamp 'A') but also a convenient tell-tale as to when a run of
washing is complete (ie: when the machine stops drawing current).

(Of course, I'm stuffed if it turns out that the machines draw
current all the time - I will check that!)

TIA,


GB
--
"Most police misconduct occurs when citizens challenge an individual
officer's authority" (Reiss, 1971 c.in Jermier & Berkes 1979)
Perhaps you could adapt a current sensing circuit for automatically
turning on periperals when a computer is switched on. There was one
published in Elektor, July/August 2004 and I've got a feeling I saw a
similar thing in one of the other mags- Silicon Chip or EPE maybe.

I also found one at:

http://sound.westhost.com/project79.htm

Andy Wood
woodag@trap.ozemail.com.au
 
"GB" <gb0807@kickindanuts.threefiddy.com> wrote in message
news:13o97hq28a9eo0c@corp.supernews.com...
Situation is a block of units with shared external laundries. Each unit
has a switch internally that energises a power point in the external
laundry.

Is it (easilyishly) possible to install a lamp (something that clips
into a standard switchplate would be nice) that illuminates only when
current is being drawn through that circuit?

snip

************* First of all it's dangerous to modify any mains high voltage
circuits unless you are a qualifed electrician ****
(ie know what you are doing)

I been in that UNIT situation.

I replace the switch with switch+light (light goes on when switch is on)
but doesn't monitor current


You could look at current clamp meter
http://en.wikipedia.org/wiki/Clamp_meter

This needs to go around one of the wires

Or

http://en.wikipedia.org/wiki/Current_transformer



Joe
 
"Giant Bullshitartist Fucking IDIOT "


Situation is a block of units with shared external laundries. Each unit
has a switch internally that energises a power point in the external
laundry.

Is it (easilyishly) possible to install a lamp (something that clips
into a standard switchplate would be nice) that illuminates only when
current is being drawn through that circuit?

** What the FUCK for - dickhead ??


The object being not only a reminder that the circuit is live (via
lamp 'A') but also a convenient tell-tale as to when a run of
washing is complete (ie: when the machine stops drawing current).

** Errr - it is blindingly fucking OBVIOUS when a washer stops drawing
current -

YOU DUMB ASS !!!


(Of course, I'm stuffed if it turns out that the machines draw all the
time ..

** Yeah - sure they do.

Even when silent, dead, stopped, unplugged - the whole fucking lot.


Gaaawd fucking almighty - when massive nuclear radiation and / or
CO2 induced global warming turn the whole damn planet to TOAST
- there will *still* be massive armies of vile cockroaches AND

FUCKING MASTURBATING IMBECILES LIKE GB !!!

Peeeeeeeuuuuuukeeeeeeeeeeeeeeeeeeee



....... Phil
 
Joe G (Home) wrote:
"GB" <gb0807@kickindanuts.threefiddy.com> wrote in message
news:13o97hq28a9eo0c@corp.supernews.com...
Situation is a block of units with shared external laundries. Each unit
has a switch internally that energises a power point in the external
laundry.

Is it (easilyishly) possible to install a lamp (something that clips
into a standard switchplate would be nice) that illuminates only when
current is being drawn through that circuit?

snip

************* First of all it's dangerous to modify any mains high voltage
circuits unless you are a qualifed electrician ****
(ie know what you are doing)

I been in that UNIT situation.

I replace the switch with switch+light (light goes on when switch is on)
but doesn't monitor current


You could look at current clamp meter
http://en.wikipedia.org/wiki/Clamp_meter

This needs to go around one of the wires

Or

http://en.wikipedia.org/wiki/Current_transformer



Joe



I think you will find that poster means an indication inside their unit
so that they dont have to travel umpteen floors to find out
 
"Phil Allison" <philallison@tpg.com.au> wrote in message
news:5ujvi4F1ie7k5U1@mid.individual.net...
"Giant Bullshitartist Fucking IDIOT "


Situation is a block of units with shared external laundries. Each unit
has a switch internally that energises a power point in the external
laundry.

Is it (easilyishly) possible to install a lamp (something that clips
into a standard switchplate would be nice) that illuminates only when
current is being drawn through that circuit?


** What the FUCK for - dickhead ??


The object being not only a reminder that the circuit is live (via
lamp 'A') but also a convenient tell-tale as to when a run of
washing is complete (ie: when the machine stops drawing current).


** Errr - it is blindingly fucking OBVIOUS when a washer stops drawing
current -

YOU DUMB ASS !!!


(Of course, I'm stuffed if it turns out that the machines draw all the
time ..


** Yeah - sure they do.

Even when silent, dead, stopped, unplugged - the whole fucking lot.


Gaaawd fucking almighty - when massive nuclear radiation and / or
CO2 induced global warming turn the whole damn planet to TOAST
- there will *still* be massive armies of vile cockroaches AND

FUCKING MASTURBATING IMBECILES LIKE GB !!!

Peeeeeeeuuuuuukeeeeeeeeeeeeeeeeeeee



...... Phil
FFS Phil, go back and read the post from the beginning. Apply a bit of
rational thought (hang on that's beyond your capacity) and it doesn't take a
degree in fucking rocket science to figure out the laundry isn't in the
poster's unit.
Without some slight wiring re-arrangement by a qualified sparky would it be
possible to easily monitor that current is being drawn from the GPO in the
laundry, presumably controlled via an isolation switch in the poster's unit.

A number of years ago EA or one of the other electronics mags published a
circuit which could be used to switch on other mains powered devices when
current flow was detected in the a.c mains input to device used as the
"control" appliance.

I couldn't see any valid reason why that type of circuit couldn't be adapted
to detect the significant current that's likely to flow in the feed to the
washing machine whilst it is in a typical washing cycle as opposed to it
being off or having completed the selected program cycle.

The logistics of legally installing one of these devices unless a
commercially available approved device exists, are probably zero.
 
"Alan Rutlidge" <don't_spam_me_rutlidge@iinet.net.au> wrote in message
news:4784e6dd$0$11958$5a62ac22@per-qv1-newsreader-01.iinet.net.au...
"Phil Allison" <philallison@tpg.com.au> wrote in message
news:5ujvi4F1ie7k5U1@mid.individual.net...

"Giant Bullshitartist Fucking IDIOT "


Situation is a block of units with shared external laundries. Each unit
has a switch internally that energises a power point in the external
laundry.

Is it (easilyishly) possible to install a lamp (something that clips
into a standard switchplate would be nice) that illuminates only when
current is being drawn through that circuit?


** What the FUCK for - dickhead ??


The object being not only a reminder that the circuit is live (via
lamp 'A') but also a convenient tell-tale as to when a run of
washing is complete (ie: when the machine stops drawing current).


** Errr - it is blindingly fucking OBVIOUS when a washer stops drawing
current -

YOU DUMB ASS !!!


(Of course, I'm stuffed if it turns out that the machines draw all the
time ..


** Yeah - sure they do.

Even when silent, dead, stopped, unplugged - the whole fucking lot.


Gaaawd fucking almighty - when massive nuclear radiation and / or
CO2 induced global warming turn the whole damn planet to TOAST
- there will *still* be massive armies of vile cockroaches AND

FUCKING MASTURBATING IMBECILES LIKE GB !!!

Peeeeeeeuuuuuukeeeeeeeeeeeeeeeeeeee



...... Phil



FFS Phil, go back and read the post from the beginning. Apply a bit of
rational thought (hang on that's beyond your capacity) and it doesn't take
a degree in fucking rocket science to figure out the laundry isn't in the
poster's unit.
Without some slight wiring re-arrangement by a qualified sparky would it
be possible to easily monitor that current is being drawn from the GPO in
the laundry, presumably controlled via an isolation switch in the poster's
unit.

A number of years ago EA or one of the other electronics mags published a
circuit which could be used to switch on other mains powered devices when
current flow was detected in the a.c mains input to device used as the
"control" appliance.

I couldn't see any valid reason why that type of circuit couldn't be
adapted to detect the significant current that's likely to flow in the
feed to the washing machine whilst it is in a typical washing cycle as
opposed to it being off or having completed the selected program cycle.

The logistics of legally installing one of these devices unless a
commercially available approved device exists, are probably zero.




Alan. If you will keep quoting Phil's filth, you only propagate it further.
Some of us find it objectionable.
 
"Suzy" <not@valid> wrote in message news:47850c79$1@dnews.tpgi.com.au...
"Alan Rutlidge" <don't_spam_me_rutlidge@iinet.net.au> wrote in message
news:4784e6dd$0$11958$5a62ac22@per-qv1-newsreader-01.iinet.net.au...

"Phil Allison" <philallison@tpg.com.au> wrote in message
news:5ujvi4F1ie7k5U1@mid.individual.net...

SNIP
Alan. If you will keep quoting Phil's filth, you only propagate it
further. Some of us find it objectionable.
and SNIP was what I meant to do just now, rather than quoting and so doing
exactly what I was whinging about! The laugh's on me!
 
"Alan Rutlidge" <don't_spam_me_rutlidge@iinet.net.au> wrote:

....

The logistics of legally installing one of these devices unless a
commercially available approved device exists, are probably zero.
You can buy such things ( example -
http://www.oneclickpower.co.uk/index.htm ) but I have not seen an
Aussie version.


Andy Wood
woodag@trap.ozemail.com.au
 
Suzy"


** YOU are a TROLLING BLOODY IDIOT

And a PITA, moronic net cop.

PISSSS OFFFFF




........ Phil
 
"Suzy the anonymous brain dead bitch "



** YOU are a TROLLING BLOODY IDIOT

And a PITA, moronic net cop.

PISSSS OFFFFF




........ Phil
 
"David L. Jones"
"Phil Allison"
"Giant Bullshitartist Fucking IDIOT "

Situation is a block of units with shared external laundries. Each unit
has a switch internally that energises a power point in the external
laundry.

Is it (easilyishly) possible to install a lamp (something that clips
into a standard switchplate would be nice) that illuminates only when
current is being drawn through that circuit?

** What the **** for - ********??

The object being not only a reminder that the circuit is live (via
lamp 'A') but also a convenient tell-tale as to when a run of
washing is complete (ie: when the machine stops drawing current).

** Errr - it is blindingly ********* OBVIOUS when a washer stops drawing
current -

But not convenient when it's several floors down in the common
basement laundry of a unit block.

** The OP is a completely clueless ass.

A kitchen timer is all he needs to alert him when the wash cycle is ( or
ought to be ) complete.




....... Phil
 
Phil Allison wrote:

** Phil Allison is a completely clueless ass.

A kitchen timer is all he needs to alert him when the wash cycle is ( or
ought to be ) complete.

If it works so well, buy one to remind yourself to take ALL your
medication.


--
Service to my country? Been there, Done that, and I've got my DD214 to
prove it.
Member of DAV #85.

Michael A. Terrell
Central Florida
 
On Jan 10, 5:31 am, woo...@trap.ozemail.com.au (Andy Wood) wrote:
"Alan Rutlidge" <don't_spam_me_rutli...@iinet.net.au> wrote:

...

The logistics of legally installing one of these devices unless a
commercially available approved device exists, are probably zero.

You can buy such things ( example -http://www.oneclickpower.co.uk/index.htm) but I have not seen an
Aussie version.

Andy Wood
woo...@trap.ozemail.com.au
Check your local Bunnings store, they have all manner of "smart" mains
devices like that, so may have something that is suitable.

Dave.
 
On Jan 10, 12:12 am, "Phil Allison" <philalli...@tpg.com.au> wrote:
"Giant Bullshitartist Fucking IDIOT "

Situation is a block of units with shared external laundries. Each unit
has a switch internally that energises a power point in the external
laundry.

Is it (easilyishly) possible to install a lamp (something that clips
into a standard switchplate would be nice) that illuminates only when
current is being drawn through that circuit?

** What the **** for - ********??

The object being not only a reminder that the circuit is live (via
lamp 'A') but also a convenient tell-tale as to when a run of
washing is complete (ie: when the machine stops drawing current).

** Errr - it is blindingly ********* OBVIOUS when a washer stops drawing
current -
But not convenient when it's several floors down in the common
basement laundry of a unit block.

Dave.
 
"Michael A. Terrell" <mike.terrell@earthlink.net> wrote in message
news:478541D4.8E24CC39@earthlink.net...
Phil Allison wrote:


** Phil Allison is a completely clueless ass.

A kitchen timer is all he needs to alert him when the wash cycle is ( or
ought to be ) complete.


If it works so well, buy one to remind yourself to take ALL your
medication.


--
Service to my country? Been there, Done that, and I've got my DD214 to
prove it.
Member of DAV #85.

Michael A. Terrell
Central Florida
OUCH!!!!
Slam dunked beautifully. :)
 
Alan Rutlidge wrote:
"Michael A. Terrell" <mike.terrell@earthlink.net> wrote in message
news:478541D4.8E24CC39@earthlink.net...

Phil Allison wrote:

** Phil Allison is a completely clueless ass.

A kitchen timer is all he needs to alert him when the wash cycle is ( or
ought to be ) complete.

If it works so well, buy one to remind yourself to take ALL your
medication.

OUCH!!!!
Slam dunked beautifully. :)

What can I say? My health is finally improving, and my sense of
humor is backkkk! :)


--
Service to my country? Been there, Done that, and I've got my DD214 to
prove it.
Member of DAV #85.

Michael A. Terrell
Central Florida
 
On Jan 9, 11:11 pm, "Joe G \(Home\)" <jo...@optusnet.com.au> wrote:
"GB" <gb0...@kickindanuts.threefiddy.com> wrote in message

news:13o97hq28a9eo0c@corp.supernews.com...> Situation is a block of units with shared external laundries. Each unit
has a switch internally that energises a power point in the external
laundry.

Is it (easilyishly) possible to install a lamp (something that clips
into a standard switchplate would be nice) that illuminates only when
current is being drawn through that circuit?

snip

************* First of all it's dangerous to modify any mains high voltage
circuits unless you are a qualifed electrician ****
(ie know what you are doing)

I been in that UNIT situation.

I replace the switch with switch+light (light goes on when switch is on)
but doesn't monitor current

You could look at current clamp meterhttp://en.wikipedia.org/wiki/Clamp_meter

This needs to go around one of the wires

Or

http://en.wikipedia.org/wiki/Current_transformer

Joe

Current transformers are often used in typical domestic PC UPS
devices, Those that I have seen usually have about 4 turns of wire
round the primary, in series with the load (on one side of the mains
output). The secondary is rectified, and monitored by the UPS to
determine the mains load, so as to act as overload protection, etc.

With a laundry, it probably be wise to use thick wire, due to startup
currents of washing machine motors, and possibility of a washing
machine/dryer being on at the same time, maybe drawing in excess of
20a continuous.
This is a lot more than a typical UPS that might be rated at anything
from 200-1000W

if you are technically minded and know what you are doing in relation
to mains wiring and safety, you could try removing the low voltage
secondary of a typical small transformer from a 240v (ironcore
transformer based ! ) plugpack and replacing the secondary (low
voltage side) with a few turns of 20a rated wire in series with the
load. Im sure you would get a usable voltage from the other side of
the transformer that you could monitor to get an idea of the current
being drawn in the laundry.

Depending on the voltage coming out under load, it could be used to
drive a LED through a suitable dropping resistor.
if the voltage is too much you can have less windings on the primary
(mains) side.


On the other hand you could try Haymans, Turks etc, they might have
something in their catalog that would do this job with much less fuss.


Remember too that since this involves direct connection to fixed
wiring doing this would certainly be illegal, if you arent a licensed
electrician, and even if you were, the device might require approval
etc.
 