NEC reference says that 12ga THHN wire can carry 30A max
current. Motor load is currently drawing constant 20A (230v
1ph circuit). Breaker is 30A.
(A bit of history: Previous motor (running from 208v) was
drawing less (15A?) current until machine broke. New
machine's motor (running from 230v via boost
autotransformer) is drawing 20A (measured at breaker).
Motor spec plate says 16A.)
Is 12ga wire sufficient, or should I bump it up to 10ga?
Would the autotransformer account for the increased current
draw?