A Mythbusters moment ...

P

Phil Allison

Guest
** Hi again,

having tested that 1.1 metre length of 10 amp rated extension lead to see
just what level of current it could pass while remaining within a safe temp
limit - it seemed I should adopt the philosophy of Jamie and Adam
Mythbuster and test exactly how much current it takes to ** COMPLETELY
DESTROY ** the same cable.

With a 50 amp capability on hand, I figured it just had to be tried !!!!

Remember, 24 amps caused the cable to reach its safe rated temperature of
75C.

When stepped up to 30 amps, there was still no sign of the cable demising
any time soon.

At 34 amps it was getting damn hot - too hot to touch, but still persisted
in working OK.

Finally, at a current of 43 amps and a surface temp of about 180C, wisps of
smoke appeared and large, ugly bubbles began to grow on the cable like
blisters PLUS where I had soldered the blue and brown wire ends together -
the solder melted. I decided to call it quits.

The cable now looks very sad and sorry indeed and has a dead short inside it
somewhere.

But I can still report that there are no exposed conductors visible.



..... Phil
 
Phil Allison wrote:
** Hi again,

having tested that 1.1 metre length of 10 amp rated extension lead to see
just what level of current it could pass while remaining within a safe temp
limit - it seemed I should adopt the philosophy of Jamie and Adam
Mythbuster and test exactly how much current it takes to ** COMPLETELY
DESTROY ** the same cable.

With a 50 amp capability on hand, I figured it just had to be tried !!!!

Remember, 24 amps caused the cable to reach its safe rated temperature of
75C.

When stepped up to 30 amps, there was still no sign of the cable demising
any time soon.

At 34 amps it was getting damn hot - too hot to touch, but still persisted
in working OK.

Finally, at a current of 43 amps and a surface temp of about 180C, wisps of
smoke appeared and large, ugly bubbles began to grow on the cable like
blisters PLUS where I had soldered the blue and brown wire ends together -
the solder melted. I decided to call it quits.

The cable now looks very sad and sorry indeed and has a dead short inside it
somewhere.

But I can still report that there are no exposed conductors visible.



.... Phil
Did you video it for Dave?
 
"Swanny" <swanny@nospam.org> wrote in message
news:CgHSn.3287$Ls1.2423@news-server.bigpond.net.au...
Phil Allison wrote:
** Hi again,

having tested that 1.1 metre length of 10 amp rated extension lead to see
just what level of current it could pass while remaining within a safe
temp
limit - it seemed I should adopt the philosophy of Jamie and Adam
Mythbuster and test exactly how much current it takes to ** COMPLETELY
DESTROY ** the same cable.

With a 50 amp capability on hand, I figured it just had to be tried !!!!

Remember, 24 amps caused the cable to reach its safe rated temperature of
75C.

When stepped up to 30 amps, there was still no sign of the cable demising
any time soon.

At 34 amps it was getting damn hot - too hot to touch, but still
persisted
in working OK.

Finally, at a current of 43 amps and a surface temp of about 180C, wisps
of
smoke appeared and large, ugly bubbles began to grow on the cable like
blisters PLUS where I had soldered the blue and brown wire ends
together -
the solder melted. I decided to call it quits.

The cable now looks very sad and sorry indeed and has a dead short inside
it
somewhere.

But I can still report that there are no exposed conductors visible.



.... Phil




Did you video it for Dave?

"It's a piece of *shit*!!!"
 
Phil Allison wrote:

having tested that 1.1 metre length of 10 amp rated extension lead to see
just what level of current it could pass while remaining within a safe temp
limit - it seemed I should adopt the philosophy of Jamie and Adam
Mythbuster and test exactly how much current it takes to ** COMPLETELY
DESTROY ** the same cable.

With a 50 amp capability on hand, I figured it just had to be tried !!!!
I have an IEC power cable that has 10A stamped on it at least several
times. Taking it apart (I have a couple of them), shows there are 22
*very* fine stands of wire (too fine to measure on calipers alone, and
still too fine to wind around a cylinder to multiply the thickness and
then divide down.

At the end of the day, I *know* what a 7.5A, and 10A KMart cable looks
like on the inside, and this is NOT anywhere in that realm.

It's clearly a chinese fake, I don't give crap who says what, you can't
defy the laws of physics just by stamping a different number on the cable.

I'm happy to donate that cable to the cause. I don't have a power
supply on hand with that much juice capability.
 
"John Tserkezis"

I have an IEC power cable that has 10A stamped on it at least several
times.

** Where did it come from ?

K-Mart ? Woollies ?? Coles??

No ?????

Lemme guess - along with a private imported product direct from Hong Kong
or China.

The IMPORTER is the person who is liable for making sure any electrical
leads supplied with equipment are legit and have the required safety
approvals.

There is no authority to complain to when YOU are the culprit.



..... Phil
 
Phil Allison wrote:

** Where did it come from ?
K-Mart ? Woollies ?? Coles??
No ?????
Nope.

Lemme guess - along with a private imported product direct from Hong Kong
or China.
This one in particular came from a yumcha computer retailer here, but
the same goes for eBay crap as well. I've seen it all round.

The IMPORTER is the person who is liable for making sure any electrical
leads supplied with equipment are legit and have the required safety
approvals.

There is no authority to complain to when YOU are the culprit.
In this case, I'm not the importer, but you seem to splitting hairs here.

Crap is crap no matter where you get it from.
I don't give a flying crap where the legal blame finger is pointed, it
doesn't make a squat of difference to me.
I'm still getting crap in a box. Either way.
 
"John Tserkezisis = Vile Wog PIG "

** Listen shithead - do NOT EVER remove the topic line !!!

Here it is again:

" I have an IEC power cable that has 10A stamped on it at least several
times. Taking it apart (I have a couple of them), shows there are 22 *very*
fine stands of wire (too fine to measure on calipers alone, and still too
fine to wind around a cylinder to multiply the thickness and then divide
down. "


** Where did it come from ?

K-Mart ? Woollies ?? Coles??

No ?????

Nope.
** Of course it didn't ............

Cos you are bullshitting your arse of - as fucking usual.


Lemme guess - along with a private imported product direct from Hong
Kong
or China.

This one in particular came from a yumcha computer retailer here,

** So now YOU are PROTECTING some stupid Chink by NOT reporting him to
the authorities ??

What a ' piece of work ' you are - you vile, wog pig.

Some poor kiddie may DIE because of YOU !!!



The IMPORTER is the person who is liable for making sure any electrical
leads supplied with equipment are legit and have the required safety
approvals.

There is no authority to complain to when YOU are the culprit.

In this case, I'm not the importer,

** So YOU are personally PROTECTING some stupid Chink by NOT reporting
him to the authorities ??

What a ' piece of work ' you are - you vile, wog PIG.

Some poor kiddie may DIE because of YOU !!!


Crap is crap no matter where you get it from.

** Everything that comes out of YOU is 100% CRAP.

Cos you are totally FULL of SHIT !!!!!!!

Some poor kiddie may DIE because of YOU !!!

YOU make me wanna PUKE !!!



..... Phil
 
kelly wrote:
"Swanny" <swanny@nospam.org> wrote in message
news:CgHSn.3287$Ls1.2423@news-server.bigpond.net.au...
Phil Allison wrote:
** Hi again,

having tested that 1.1 metre length of 10 amp rated extension lead
to see just what level of current it could pass while remaining
within a safe temp
limit - it seemed I should adopt the philosophy of Jamie and Adam
Mythbuster and test exactly how much current it takes to **
COMPLETELY DESTROY ** the same cable.

With a 50 amp capability on hand, I figured it just had to be tried
!!!! Remember, 24 amps caused the cable to reach its safe rated
temperature of 75C.

When stepped up to 30 amps, there was still no sign of the cable
demising any time soon.

At 34 amps it was getting damn hot - too hot to touch, but still
persisted
in working OK.

Finally, at a current of 43 amps and a surface temp of about 180C,
wisps of
smoke appeared and large, ugly bubbles began to grow on the cable
like blisters PLUS where I had soldered the blue and brown wire
ends together -
the solder melted. I decided to call it quits.

The cable now looks very sad and sorry indeed and has a dead short
inside it
somewhere.

But I can still report that there are no exposed conductors visible.



.... Phil




Did you video it for Dave?


"It's a piece of *shit*!!!"
I'm coming up to my 100th episode were I'll probably do a recap from each
one. Will be interesting to see how many times that phrase comes out!

Dave.

--
================================================
Check out my Electronics Engineering Video Blog & Podcast:
http://www.eevblog.com
 
"David L. Jones" <altzone@gmail.com> wrote in message
news:vZyTn.17213$3y2.15674@newsfe11.iad...
kelly wrote:
"Swanny" <swanny@nospam.org> wrote in message
news:CgHSn.3287$Ls1.2423@news-server.bigpond.net.au...
Phil Allison wrote:
** Hi again,

having tested that 1.1 metre length of 10 amp rated extension lead
to see just what level of current it could pass while remaining
within a safe temp
limit - it seemed I should adopt the philosophy of Jamie and Adam
Mythbuster and test exactly how much current it takes to **
COMPLETELY DESTROY ** the same cable.

With a 50 amp capability on hand, I figured it just had to be tried
!!!! Remember, 24 amps caused the cable to reach its safe rated
temperature of 75C.

When stepped up to 30 amps, there was still no sign of the cable
demising any time soon.

At 34 amps it was getting damn hot - too hot to touch, but still
persisted
in working OK.

Finally, at a current of 43 amps and a surface temp of about 180C,
wisps of
smoke appeared and large, ugly bubbles began to grow on the cable
like blisters PLUS where I had soldered the blue and brown wire
ends together -
the solder melted. I decided to call it quits.

The cable now looks very sad and sorry indeed and has a dead short
inside it
somewhere.

But I can still report that there are no exposed conductors visible.



.... Phil




Did you video it for Dave?


"It's a piece of *shit*!!!"

I'm coming up to my 100th episode were I'll probably do a recap from each
one. Will be interesting to see how many times that phrase comes out!

Dave.

--
================================================
Check out my Electronics Engineering Video Blog & Podcast:
http://www.eevblog.com
Keep it up, it's entertaining & I learn the odd thing! Maybe go to
fortnightly so you don't runout/burnout.
 