Sammo
Guest

Sat Feb 12, 2005 12:09 pm   



I am in the UK (so mains voltage is about 230V or 240V).

I have a reel of main extension cable made of 3-core 1.0 mm^2 wire
rated at 10 Amps. So the nominal power rating would be about 2,400
Watts. (Link to tech reference for the cable is below.)

Presumably the current carrying capacity or power delivery
capability of the unwound 30m length unwound is going to be a bit
less than 10 Amps/2,400 Watts due to losses along the length of the
cable itself.

Is the reduction in current/power carrying capability significant?
If so, then is there a rough guideline figure for available
current/power which I can use?

If I take *two* of these 30m reels then I can join them with the
standard UK 13 Amp plug and socket supplied on the reels. This gives
me an overall length of 60m. Taking into account losses, what would
be the current carrying or power delivery carrying capability of the
60m length if all the 60m cable is unwound?

Thanks for any info.
Sammo


Technical reference for the cable is HAR type H05VV-F3 x 1.00 mm2 -
(details at http://tinyurl.com/7y5xx)

Ian Stirling
Guest

Sat Feb 12, 2005 12:46 pm   



In uk.d-i-y Sammo <noone_at_no-where.com> wrote:
Quote:
I am in the UK (so mains voltage is about 230V or 240V).

I have a reel of main extension cable made of 3-core 1.0 mm^2 wire
rated at 10 Amps. So the nominal power rating would be about 2,400
Watts. (Link to tech reference for the cable is below.)

It's always going to be safe, as it's got a fuse.

Ok...
Copper has a resistivity of 0.7*10^-8 ohms/meter.

Or, for a 1mm^2 wire, 0.7*10^-2 ohms/meter.
Or for 2 wires, 1.4*10^-2 ohms.
Or for 60m, 8.4*10^-1 ohms, or .84 ohms.
At 10A, 8.4V, or heating by 84W.
If at the plug end is 240V, at the socket end will be 232V, which is
(232^2/240^2)= .93444444444444444444

So, you lose 7% of the power for a heater, for example.

Ian Stirling
Guest

Sat Feb 12, 2005 12:54 pm   



In uk.d-i-y Ian Stirling <root_at_mauve.demon.co.uk> wrote:
Quote:
In uk.d-i-y Sammo <noone_at_no-where.com> wrote:
I am in the UK (so mains voltage is about 230V or 240V).

I have a reel of main extension cable made of 3-core 1.0 mm^2 wire
rated at 10 Amps. So the nominal power rating would be about 2,400
Watts. (Link to tech reference for the cable is below.)

It's always going to be safe, as it's got a fuse.

Ok...
Copper has a resistivity of 0.7*10^-8 ohms/meter.

Doh, 1.7.
Quote:

Or, for a 1mm^2 wire, 0.7*10^-2 ohms/meter.
1.7*10^-2
Or for 2 wires, 1.4*10^-2 ohms.
3.4*10^-2


Quote:
Or for 60m, 8.4*10^-1 ohms, or .84 ohms.

2 ohms.

At 10A, 20V, or the cable heating by 200W.
If at the plug end is 240V, at the socket end will be 220V, which is
(220^2/240^2)= .84027777777777777777

So, you lose 16% of the power for a heater, for example.

Bob Eager
Guest

Sat Feb 12, 2005 1:18 pm   



On Sat, 12 Feb 2005 12:46:19 UTC, Ian Stirling <root_at_mauve.demon.co.uk>
wrote:

Quote:
Or for 60m, 8.4*10^-1 ohms, or .84 ohms.

Plus the resistance on the two connections. Not sure whether the earth
fault loop impedance is still OK...

--
Bob Eager
begin a new life...dump Windows!

Ian Stirling
Guest

Sat Feb 12, 2005 1:59 pm   



In uk.d-i-y Bob Eager <rde42_at_spamcop.net> wrote:
Quote:
On Sat, 12 Feb 2005 12:46:19 UTC, Ian Stirling <root_at_mauve.demon.co.uk
wrote:

Or for 60m, 8.4*10^-1 ohms, or .84 ohms.

Plus the resistance on the two connections. Not sure whether the earth
fault loop impedance is still OK...

I took that into account. (but misremembered the resistivity of copper)
See other post for correction.

Palindr☻me
Guest

Sat Feb 12, 2005 2:47 pm   



Palindr☻me wrote:

Quote:
Sammo wrote:

I am in the UK (so mains voltage is about 230V or 240V).

I have a reel of main extension cable made of 3-core 1.0 mm^2 wire
rated at 10 Amps. So the nominal power rating would be about 2,400
Watts. (Link to tech reference for the cable is below.)

Presumably the current carrying capacity or power delivery capability
of the unwound 30m length unwound is going to be a bit less than 10
Amps/2,400 Watts due to losses along the length of the cable itself.
Is the reduction in current/power carrying capability significant? If
so, then is there a rough guideline figure for available current/power
which I can use?

If I take *two* of these 30m reels then I can join them with the
standard UK 13 Amp plug and socket supplied on the reels. This gives
me an overall length of 60m. Taking into account losses, what would
be the current carrying or power delivery carrying capability of the
60m length if all the 60m cable is unwound?


30 metres at 10 amperes isn't going to be a problem - so I have
considered just the longer lengths.

Basically, you have two factors to consider:

The first is how hot the wire will get. Now, provided that the cable is
unwound and in the open air, then its length is immaterial. If you coil
the cable up or cover it in something that restricts the flow of heat
from it, that is a different matter. However, for an unwound cable, the
rated current, say 10 amperes, is the maximum that is allowed due to
heat constraints. Pass more current than this and the wire will get too
hot. Pass a lot more current than this and the insulation could fail.

The second is the volt drop. Its resistance is about 0.02 ohms per metre
- so a 60 m length will have a resistance of 1.2 ohms and will drop 1.2
volts per ampere. A 120 m length would drop 2.4 volts per ampere.

Now the equipment at the far end of the cable will have a specified
range of input voltage for which it was designed. You must simply ensure
that it gets the minimum rated voltage, or higher, at the current it
draws. This minimum voltage will depend on the equipment type.

As a rough guide, losing 12 volts in 240 is probably going to be fine.
So, you could use a 60 metre cable at 10 amperes or 120 metre cable at 5
amperes.

If your load is happier with a lower minimum voltage, say 220 volts,
then you could run the 120m cable at about 8 amperes. However, you would
still be limited to 10 amperes for the 60 metre cable, because 10
amperes is the most the cable should be used to carry, irrespective of
length.

Purely resistive loads, like heaters, aren't terribly fussed if their
voltage is a bit low - so you could happily run a 2kW heater at the end
of 120 metres of your cable. If you have a lamp plugged in at the far
end, then it will get noticeably dimmer when the heater is switched on.
This isn't a safety problem, although it might appear so.

Some loads are very fussy about their minimum voltage but even those
should be happy with 10 amperes taken from your 60 metre cable.




OOPs! Yes, I forgot it was twin flex.

Ignore my last post - I clearly shouldn't have got up so
eary this morning...and will now correct that error. Well,
it was a good party last night, from what I remember.

--

Sue

John Rumm
Guest

Sat Feb 12, 2005 2:56 pm   



Ian Stirling wrote:

Quote:
Short current is some 120A, plenty to blow a 10A fuse quite prombtly.

You are assuming that the supply impeadance is zero however. If you
factor that in, then you drop the PSC a bit...

(Still ought to be plenty to blow a 13A fuse in under a second though)


--
Cheers,

John.

/=================================================================\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\=================================================================/

Dave Plowman (News)
Guest

Sat Feb 12, 2005 3:11 pm   



In article <376fo9F59cjg9U3_at_individual.net>,
Palindr☻me <sb382638_at_hotmail.com.invalid> wrote:
Quote:
OOPs! Yes, I forgot it was twin flex.

3 core, actually. ;-)

--
*Happiness is seeing your mother-in-law on a milk carton

Dave Plowman dave_at_davenoise.co.uk London SW
To e-mail, change noise into sound.

Palindr☻me
Guest

Sat Feb 12, 2005 3:17 pm   



Sammo wrote:

Quote:
I am in the UK (so mains voltage is about 230V or 240V).

I have a reel of main extension cable made of 3-core 1.0 mm^2 wire
rated at 10 Amps. So the nominal power rating would be about 2,400
Watts. (Link to tech reference for the cable is below.)

Presumably the current carrying capacity or power delivery
capability of the unwound 30m length unwound is going to be a bit
less than 10 Amps/2,400 Watts due to losses along the length of the
cable itself.

Is the reduction in current/power carrying capability significant?
If so, then is there a rough guideline figure for available
current/power which I can use?

If I take *two* of these 30m reels then I can join them with the
standard UK 13 Amp plug and socket supplied on the reels. This gives
me an overall length of 60m. Taking into account losses, what would
be the current carrying or power delivery carrying capability of the
60m length if all the 60m cable is unwound?

30 metres at 10 amperes isn't going to be a problem - so I
have considered just the longer lengths.

Basically, you have two factors to consider:

The first is how hot the wire will get. Now, provided that
the cable is unwound and in the open air, then its length is
immaterial. If you coil the cable up or cover it in
something that restricts the flow of heat from it, that is a
different matter. However, for an unwound cable, the rated
current, say 10 amperes, is the maximum that is allowed due
to heat constraints. Pass more current than this and the
wire will get too hot. Pass a lot more current than this and
the insulation could fail.

The second is the volt drop. Its resistance is about 0.02
ohms per metre - so a 60 m length will have a resistance of
1.2 ohms and will drop 1.2 volts per ampere. A 120 m length
would drop 2.4 volts per ampere.

Now the equipment at the far end of the cable will have a
specified range of input voltage for which it was designed.
You must simply ensure that it gets the minimum rated
voltage, or higher, at the current it draws. This minimum
voltage will depend on the equipment type.

As a rough guide, losing 12 volts in 240 is probably going
to be fine. So, you could use a 60 metre cable at 10 amperes
or 120 metre cable at 5 amperes.

If your load is happier with a lower minimum voltage, say
220 volts, then you could run the 120m cable at about 8
amperes. However, you would still be limited to 10 amperes
for the 60 metre cable, because 10 amperes is the most the
cable should be used to carry, irrespective of length.

Purely resistive loads, like heaters, aren't terribly fussed
if their voltage is a bit low - so you could happily run a
2kW heater at the end of 120 metres of your cable. If you
have a lamp plugged in at the far end, then it will get
noticeably dimmer when the heater is switched on. This isn't
a safety problem, although it might appear so.

Some loads are very fussy about their minimum voltage but
even those should be happy with 10 amperes taken from your
60 metre cable.

Hope that helps.

Sue

Owain
Guest

Sat Feb 12, 2005 3:44 pm   





Interfacebus.com
Guest

Sat Feb 12, 2005 4:02 pm   





Ian Stirling
Guest

Sat Feb 12, 2005 4:22 pm   





Dave Plowman (News)
Guest

Sat Feb 12, 2005 5:10 pm   





Andrew Chesters
Guest

Sat Feb 12, 2005 5:35 pm   






Guest

Sat Feb 12, 2005 6:26 pm   





Goto page 1, 2, 3, 4, 5, 6  Next

elektroda.net NewsGroups Forum Index - Electronics Equipment - How much current safe for 30m extension?

Ask a question - edaboard.com

Arabic versionBulgarian versionCatalan versionCzech versionDanish versionGerman versionGreek versionEnglish versionSpanish versionFinnish versionFrench versionHindi versionCroatian versionIndonesian versionItalian versionHebrew versionJapanese versionKorean versionLithuanian versionLatvian versionDutch versionNorwegian versionPolish versionPortuguese versionRomanian versionRussian versionSlovak versionSlovenian versionSerbian versionSwedish versionTagalog versionUkrainian versionVietnamese versionChinese version