Goto page 1, 2, 3, 4, 5, 6, 7, 8, 9 Next
John Fields
Guest
Thu Oct 21, 2010 9:01 pm
On Thu, 21 Oct 2010 10:47:50 -0400, "Jon" <jon8338_at_peoplepc.com>
wrote:
Quote:
http://jons-math.bravehost.com/transfercircuit.html
---
Which relay are you using? (manufacturer/part number)
---
JF
PeterD
Guest
Thu Oct 21, 2010 11:29 pm
On Thu, 21 Oct 2010 10:47:50 -0400, "Jon" <jon8338_at_peoplepc.com>
wrote:
Quote:
http://jons-math.bravehost.com/transfercircuit.html
Idiot...
Learn the difference between ground and neutral. You don't switch
ground.
Idiot...
Troll...
Jim Rojas
Guest
Fri Oct 22, 2010 12:16 am
PeterD wrote:
Quote:
He's right. Also note that the grounds need to be within a few feet of
each generator, as per the National Electrical Code. This means
installing a ground rod at each generator to be in compliance.
Jim Rojas
Jim Rojas
Guest
Fri Oct 22, 2010 12:26 am
PeterD wrote:
Quote:
Sorry, I missed the diagram below. Just ground the generator by
installing a grounding rod within 5 feet of it, the rest of the grounds
can be bonded together, as well as to the box itself. Do not attach the
grounds in any way to your relay.
Jim Rojas
Martin Riddle
Guest
Fri Oct 22, 2010 1:04 am
"PeterD" <peter2_at_hipson.net> wrote in message
news:pkf1c69u4g0vdvrg0vik2mgnr54s6bpu5b_at_4ax.com...
Quote:
Correct, For a transfer switch you do switch Neutral, not ground.
Cheers
Proteus
Guest
Fri Oct 22, 2010 4:33 am
On Oct 21, 8:04 pm, "Martin Riddle" <martin_...@verizon.net> wrote:
Quote:
"PeterD" <pet...@hipson.net> wrote in message
news:pkf1c69u4g0vdvrg0vik2mgnr54s6bpu5b_at_4ax.com...
On Thu, 21 Oct 2010 10:47:50 -0400, "Jon" <jon8...@peoplepc.com
wrote:
http://jons-math.bravehost.com/transfercircuit.html
Idiot...
Learn the difference between ground and neutral. You don't switch
ground.
Idiot...
Troll...
Correct, For a transfer switch you do switch Neutral, not ground.
Cheers
THE DIAGRAM CONTAINS A RELAY WITH FULL ELECTRICAL TRANSFER CAPACITY
THE LINE PLUS THE GROUND
THE GROUND SHOULD BE CONNECTED AS WELL
AND LEFT TO TRANSFER WITH THE LOAD
THOUGH THE GEN CAN BE SEPARATELY GROUNDED WITH A ROD AS SUGGESTED
DO NOT TIE OR SPLICE THE GROUND TOGETHER AS SUGGESTED
THE GROUND COULD BECOME COMPROMISED UPSTREAM AND DAMAGE THE CONTROL
UNIT
WITH THE GRND OPEN [UNTIL RELAYED]
THE GEN AND CONTROL CIRCUITS ARE PROTECTED FOR FLOATING 100% OFF THE
SYSTEM
I AM PROTEUS
Proteus
Guest
Fri Oct 22, 2010 6:21 am
"Martin Riddle" <martin_rid_at_verizon.net> wrote in message
news:i9qklm$mn9$3_at_news.eternal-september.org...
Quote:
"PeterD" <peter2_at_hipson.net> wrote in message
news:pkf1c69u4g0vdvrg0vik2mgnr54s6bpu5b_at_4ax.com...
On Thu, 21 Oct 2010 10:47:50 -0400, "Jon" <jon8338_at_peoplepc.com
wrote:
http://jons-math.bravehost.com/transfercircuit.html
Idiot...
Learn the difference between ground and neutral. You don't switch
ground.
Idiot...
Troll...
Correct, For a transfer switch you do switch Neutral, not ground.
Cheers
No dumbasses PeterDumb, you are always dumb as usual, and Martin follows
the same Skunk ever since PeterDumb made lousy comment last time on Jon.
Jon is right.
Jim Rojas maybe new but he's down to earth.
Why you want to switch ground on the generator ground? Because it's the same
Ground that you dumbasses refer to "Neutral", better switch on copper nearby
than a ground far away.
I recommend connect both Neutral and Generator ground together. Then double
a pair of switch contact to Hot, this will double current capacity.
Heehee.......
I AM PROIDIOT
PeterD
Guest
Fri Oct 22, 2010 1:37 pm
On Thu, 21 Oct 2010 22:21:40 -0700, "Proteus"
<arcturian1_at_earthlink.net> wrote:
Quote:
No dumbasses PeterDumb, you are always dumb as usual, and Martin follows
the same Skunk ever since PeterDumb made lousy comment last time on Jon.
Jon is right.
Jim Rojas maybe new but he's down to earth.
Why you want to switch ground on the generator ground? Because it's the same
Ground that you dumbasses refer to "Neutral", better switch on copper nearby
than a ground far away.
I recommend connect both Neutral and Generator ground together. Then double
a pair of switch contact to Hot, this will double current capacity.
Heehee.......
I AM PROIDIOT
Like that signature...
And glad I don't live anywhere near you...
Proteus
Guest
Fri Oct 22, 2010 4:42 pm
"Proteus" <proteusiiv_at_gmail.com> wrote in message
news:a94b6c58-52ef-4de5-9199-c838b291adc3_at_u10g2000yqk.googlegroups.com...
On Oct 22, 1:21 am, "Proteus" <arcturi...@earthlink.net> wrote:
Quote:
"Martin Riddle" <martin_...@verizon.net> wrote in message
news:i9qklm$mn9$3_at_news.eternal-september.org...
"PeterD" <pet...@hipson.net> wrote in message
news:pkf1c69u4g0vdvrg0vik2mgnr54s6bpu5b_at_4ax.com...
On Thu, 21 Oct 2010 10:47:50 -0400, "Jon" <jon8...@peoplepc.com
wrote:
http://jons-math.bravehost.com/transfercircuit.html
Idiot...
Learn the difference between ground and neutral. You don't switch
ground.
Idiot...
Troll...
Correct, For a transfer switch you do switch Neutral, not ground.
Cheers
No dumbasses PeterDumb, you are always dumb as usual, and Martin follows
the same Skunk ever since PeterDumb made lousy comment last time on Jon.
Jon is right.
Jim Rojas maybe new but he's down to earth.
Why you want to switch ground on the generator ground? Because it's the
same
Ground that you dumbasses refer to "Neutral", better switch on copper
nearby
than a ground far away.
I recommend connect both Neutral and Generator ground together. Then
double
a pair of switch contact to Hot, this will double current capacity.
Heehee.......
I AM PROIDIOT
SOMEBODY AUGHT TO SLAP THE STUPID OUT OF YOU
I AM PROTEUS
I just prove that you dumbasses are wrong again, you claimed bigger wire
doesn't carry a larger amount of current?
HEEHEE.....STUPID OR NOT, IT USUALLY BELONGS TO THE ONE CALLING OTHERS OF
BEING STUPID...
YOU LACK EXPERIENCE AND KNOWLEDGE, YES MOST OF YOU, EVEN THE ONES WITH PE.
I HAVE PROVEN TIME AFTER TIME THAT THERE IS ALWAYS ROOM TO IMPROVE YOUR
FUNKY PRODUCTS OUT THERE.
I doubled power of everything you dumbasses designed, by 10X No kidding!!
From a car charger to anything you can name, including Car performance, Fuel
efficiency, Power Generator, Semiconductor etc.
I don't share or give any thing good to you dumbasses to benefit from. Why?
Because I am not for money, and I am protecting the innocent citizens from
your abusive use of my idea/product. You're lucky that I shared some.
Proteus
Guest
Fri Oct 22, 2010 5:36 pm
On Oct 22, 1:21 am, "Proteus" <arcturi...@earthlink.net> wrote:
Quote:
"Martin Riddle" <martin_...@verizon.net> wrote in message
news:i9qklm$mn9$3_at_news.eternal-september.org...
"PeterD" <pet...@hipson.net> wrote in message
news:pkf1c69u4g0vdvrg0vik2mgnr54s6bpu5b_at_4ax.com...
On Thu, 21 Oct 2010 10:47:50 -0400, "Jon" <jon8...@peoplepc.com
wrote:
http://jons-math.bravehost.com/transfercircuit.html
Idiot...
Learn the difference between ground and neutral. You don't switch
ground.
Idiot...
Troll...
Correct, For a transfer switch you do switch Neutral, not ground.
Cheers
No dumbasses PeterDumb, you are always dumb as usual, and Martin follows
the same Skunk ever since PeterDumb made lousy comment last time on Jon.
Jon is right.
Jim Rojas maybe new but he's down to earth.
Why you want to switch ground on the generator ground? Because it's the same
Ground that you dumbasses refer to "Neutral", better switch on copper nearby
than a ground far away.
I recommend connect both Neutral and Generator ground together. Then double
a pair of switch contact to Hot, this will double current capacity.
Heehee.......
I AM PROIDIOT
SOMEBODY AUGHT TO SLAP THE STUPID OUT OF YOU
I AM PROTEUS
Proteus
Guest
Fri Oct 22, 2010 7:13 pm
On Oct 22, 11:42 am, "Proteus" <arcturi...@earthlink.net> wrote:
Quote:
"Proteus" <proteus...@gmail.com> wrote in message
news:a94b6c58-52ef-4de5-9199-c838b291adc3_at_u10g2000yqk.googlegroups.com...
On Oct 22, 1:21 am, "Proteus" <arcturi...@earthlink.net> wrote:
"Martin Riddle" <martin_...@verizon.net> wrote in message
news:i9qklm$mn9$3_at_news.eternal-september.org...
"PeterD" <pet...@hipson.net> wrote in message
news:pkf1c69u4g0vdvrg0vik2mgnr54s6bpu5b_at_4ax.com...
On Thu, 21 Oct 2010 10:47:50 -0400, "Jon" <jon8...@peoplepc.com
wrote:
http://jons-math.bravehost.com/transfercircuit.html
Idiot...
Learn the difference between ground and neutral. You don't switch
ground.
Idiot...
Troll...
Correct, For a transfer switch you do switch Neutral, not ground.
Cheers
No dumbasses PeterDumb, you are always dumb as usual, and Martin follows
the same Skunk ever since PeterDumb made lousy comment last time on Jon..
Jon is right.
Jim Rojas maybe new but he's down to earth.
Why you want to switch ground on the generator ground? Because it's the
same
Ground that you dumbasses refer to "Neutral", better switch on copper
nearby
than a ground far away.
I recommend connect both Neutral and Generator ground together. Then
double
a pair of switch contact to Hot, this will double current capacity.
Heehee.......
I AM PROIDIOT
SOMEBODY AUGHT TO SLAP THE STUPID OUT OF YOU
I AM PROTEUS
I just prove that you dumbasses are wrong again, you claimed bigger wire
doesn't carry a larger amount of current?
HEEHEE.....STUPID OR NOT, IT USUALLY BELONGS TO THE ONE CALLING OTHERS OF
BEING STUPID...
YOU LACK EXPERIENCE AND KNOWLEDGE, YES MOST OF YOU, EVEN THE ONES WITH PE..
I HAVE PROVEN TIME AFTER TIME THAT THERE IS ALWAYS ROOM TO IMPROVE YOUR
FUNKY PRODUCTS OUT THERE.
I doubled power of everything you dumbasses designed, by 10X No kidding!!
From a car charger to anything you can name, including Car performance, Fuel
efficiency, Power Generator, Semiconductor etc.
I don't share or give any thing good to you dumbasses to benefit from. Why?
Because I am not for money, and I am protecting the innocent citizens from
your abusive use of my idea/product. You're lucky that I shared some.
YOU ARE TROLLING MICHAEL TERRELL
YOU ARE DAMAGING TO THIS GROUP
YOUR INTENTIONS QUESTIONABLE AND OFFENSIVE
A COMPLAINT HAS BEEN FILED WITH YOUR ISP AND GOOGLE GROUPS FOR USING
MY MEMBERSHIP NAME AND POSTING ANNOYING FLAMING AND OFFENSIVE OFF
TOPIC RESPONSES TO THIS GROUP
YOU ARE IN VIOLATION OF THE TOS OF BOTH THIS GROUP AND YOU ISP
IF YOU DO NOT CEASE THE SPECIFIC ACTIVITY AND WRONGFUL USE OF MY
MEMBERSHIP NYM
YOU WILL BE STOPPED TROLL
I AM PROTEUS
PeterD
Guest
Fri Oct 22, 2010 11:03 pm
On Fri, 22 Oct 2010 08:42:15 -0700, "Proteus"
<arcturian1_at_earthlink.net> wrote:
Quote:
I just prove that you dumbasses are wrong again, you claimed bigger wire
doesn't carry a larger amount of current?
I didn't. Perhaps you should adjust your meds again.
Quote:
HEEHEE.....STUPID OR NOT, IT USUALLY BELONGS TO THE ONE CALLING OTHERS OF
BEING STUPID...
OK, that's your excuse... OK, we'll ignore you then.
Quote:
YOU LACK EXPERIENCE AND KNOWLEDGE, YES MOST OF YOU, EVEN THE ONES WITH PE.
I HAVE PROVEN TIME AFTER TIME THAT THERE IS ALWAYS ROOM TO IMPROVE YOUR
FUNKY PRODUCTS OUT THERE.
Coming from one who posted nothing of substance, and simply relied on
troll-like name calling? Yea, right, good move.
Quote:
I doubled power of everything you dumbasses designed, by 10X No kidding!!
From a car charger to anything you can name, including Car performance, Fuel
efficiency, Power Generator, Semiconductor etc.
Good. Got pictures?
Quote:
I don't share or give any thing good to you dumbasses to benefit from. Why?
Because it is useless and designed just like Jon's crap? Is that it?
Quote:
Because I am not for money, and I am protecting the innocent citizens from
your abusive use of my idea/product. You're lucky that I shared some.
Where? I saw nothing shared.
Jamie
Guest
Fri Oct 22, 2010 11:49 pm
Proteus wrote:
Quote:
"Proteus" <proteusiiv_at_gmail.com> wrote in message
news:a94b6c58-52ef-4de5-9199-c838b291adc3_at_u10g2000yqk.googlegroups.com...
On Oct 22, 1:21 am, "Proteus" <arcturi...@earthlink.net> wrote:
"Martin Riddle" <martin_...@verizon.net> wrote in message
news:i9qklm$mn9$3_at_news.eternal-september.org...
"PeterD" <pet...@hipson.net> wrote in message
news:pkf1c69u4g0vdvrg0vik2mgnr54s6bpu5b_at_4ax.com...
On Thu, 21 Oct 2010 10:47:50 -0400, "Jon" <jon8...@peoplepc.com
wrote:
http://jons-math.bravehost.com/transfercircuit.html
Idiot...
Learn the difference between ground and neutral. You don't switch
ground.
Idiot...
Troll...
Correct, For a transfer switch you do switch Neutral, not ground.
Cheers
No dumbasses PeterDumb, you are always dumb as usual, and Martin follows
the same Skunk ever since PeterDumb made lousy comment last time on Jon.
Jon is right.
Jim Rojas maybe new but he's down to earth.
Why you want to switch ground on the generator ground? Because it's
the same
Ground that you dumbasses refer to "Neutral", better switch on copper
nearby
than a ground far away.
I recommend connect both Neutral and Generator ground together. Then
double
a pair of switch contact to Hot, this will double current capacity.
Heehee.......
I AM PROIDIOT
SOMEBODY AUGHT TO SLAP THE STUPID OUT OF YOU
I AM PROTEUS
I just prove that you dumbasses are wrong again, you claimed bigger wire
doesn't carry a larger amount of current?
HEEHEE.....STUPID OR NOT, IT USUALLY BELONGS TO THE ONE CALLING OTHERS
OF BEING STUPID...
YOU LACK EXPERIENCE AND KNOWLEDGE, YES MOST OF YOU, EVEN THE ONES WITH
PE. I HAVE PROVEN TIME AFTER TIME THAT THERE IS ALWAYS ROOM TO IMPROVE
YOUR FUNKY PRODUCTS OUT THERE.
I doubled power of everything you dumbasses designed, by 10X No
kidding!! From a car charger to anything you can name, including Car
performance, Fuel efficiency, Power Generator, Semiconductor etc.
I don't share or give any thing good to you dumbasses to benefit from.
Why? Because I am not for money, and I am protecting the innocent
citizens from your abusive use of my idea/product. You're lucky that I
shared some.
Ooou.. I feel so honored..!
--
"I'd rather have a bottle in front of me than a frontal lobotomy"
"Daily Thought:
SOME PEOPLE ARE LIKE SLINKIES. NOT REALLY GOOD FOR ANYTHING BUT
THEY BRING A SMILE TO YOUR FACE WHEN PUSHED DOWN THE STAIRS.
http://webpages.charter.net/jamie_5"
Jamie
Guest
Fri Oct 22, 2010 11:59 pm
Proteus wrote:
Quote:
On Oct 22, 11:42 am, "Proteus" <arcturi...@earthlink.net> wrote:
"Proteus" <proteus...@gmail.com> wrote in message
news:a94b6c58-52ef-4de5-9199-c838b291adc3_at_u10g2000yqk.googlegroups.com...
On Oct 22, 1:21 am, "Proteus" <arcturi...@earthlink.net> wrote:
"Martin Riddle" <martin_...@verizon.net> wrote in message
news:i9qklm$mn9$3_at_news.eternal-september.org...
"PeterD" <pet...@hipson.net> wrote in message
news:pkf1c69u4g0vdvrg0vik2mgnr54s6bpu5b_at_4ax.com...
On Thu, 21 Oct 2010 10:47:50 -0400, "Jon" <jon8...@peoplepc.com
wrote:
http://jons-math.bravehost.com/transfercircuit.html
Idiot...
Learn the difference between ground and neutral. You don't switch
ground.
Idiot...
Troll...
Correct, For a transfer switch you do switch Neutral, not ground.
Cheers
No dumbasses PeterDumb, you are always dumb as usual, and Martin follows
the same Skunk ever since PeterDumb made lousy comment last time on Jon.
Jon is right.
Jim Rojas maybe new but he's down to earth.
Why you want to switch ground on the generator ground? Because it's the
same
Ground that you dumbasses refer to "Neutral", better switch on copper
nearby
than a ground far away.
I recommend connect both Neutral and Generator ground together. Then
double
a pair of switch contact to Hot, this will double current capacity.
Heehee.......
I AM PROIDIOT
SOMEBODY AUGHT TO SLAP THE STUPID OUT OF YOU
I AM PROTEUS
I just prove that you dumbasses are wrong again, you claimed bigger wire
doesn't carry a larger amount of current?
HEEHEE.....STUPID OR NOT, IT USUALLY BELONGS TO THE ONE CALLING OTHERS OF
BEING STUPID...
YOU LACK EXPERIENCE AND KNOWLEDGE, YES MOST OF YOU, EVEN THE ONES WITH PE.
I HAVE PROVEN TIME AFTER TIME THAT THERE IS ALWAYS ROOM TO IMPROVE YOUR
FUNKY PRODUCTS OUT THERE.
I doubled power of everything you dumbasses designed, by 10X No kidding!!
From a car charger to anything you can name, including Car performance, Fuel
efficiency, Power Generator, Semiconductor etc.
I don't share or give any thing good to you dumbasses to benefit from. Why?
Because I am not for money, and I am protecting the innocent citizens from
your abusive use of my idea/product. You're lucky that I shared some.
YOU ARE TROLLING MICHAEL TERRELL
YOU ARE DAMAGING TO THIS GROUP
YOUR INTENTIONS QUESTIONABLE AND OFFENSIVE
A COMPLAINT HAS BEEN FILED WITH YOUR ISP AND GOOGLE GROUPS FOR USING
MY MEMBERSHIP NAME AND POSTING ANNOYING FLAMING AND OFFENSIVE OFF
TOPIC RESPONSES TO THIS GROUP
YOU ARE IN VIOLATION OF THE TOS OF BOTH THIS GROUP AND YOU ISP
IF YOU DO NOT CEASE THE SPECIFIC ACTIVITY AND WRONGFUL USE OF MY
MEMBERSHIP NYM
YOU WILL BE STOPPED TROLL
I AM PROTEUS
Now if you were able to perform that cynical, diabolical task? That
would impress me! :)
Jamie.. (John Holmes/LongDong Silver!)
Goto page 1, 2, 3, 4, 5, 6, 7, 8, 9 Next